    Air Handler
    I have a Trane heat pump and air handler. When I select heat, the blower does NOT run, but the outside unit fan turns very slow and the breaker trips. Do I have a problem with the handler blower or the outside unit? Should the handler blower run when the thermostat is selected to "ON" regardless of the outside unit, or are they connected via a circuit board? Thanks for any assistance.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Dec 28, 2007, 09:36 PM
    When you put tstat on fan instead of auto,, the fan should run,, even without the H/P not running,check or have someone check all your power connections,to me good and tight,especially the grounds, the kicking of breakers is not a good sign,, when did it last work right? when the heat pump runs, the air handler fan should run at same time,the blower not blowing might be causing the h/p to kick breaker from too much high pressure,, don`t try to run till repaired
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Dec 28, 2007, 10:01 PM
    You may have more than one problem. Starting with the easiest. Turn the heat, off, cool switch to off. Turn the fan auto, on to on. If the blower doesn't come on, check the breaker to the air handler. If you have a meter, check for 24 volts AC between com and G at the air handler. If not, check your connections at both ends of the thermostat cable. See https://www.askmehelpdesk.com/heatin...ons-58313.html
    Make sure the thermostat is wired up correctly.

    If everything is OK, you may have a bad board or a bad blower motor. It is a pain getting to the contacts on the circuit board. With a voltage detector, you can just jab it into the wires running to the blower motor. If it lights up. And the motor isn't running, chances are it is bad.

    To do simple checks like this you do need some tools. A test light, a meter, or a voltage detector might be the best place to start with. I came across the niftiest gadget for trouble shooting, a voltage detector. They work through the insulation of wires. There are several brands. I have a GB Instruments GVD-505A, less than $15 at Home Depot. Touch it to a hot wire, and the end glows red. Find the doodad that lights it on one side, and not the other, and you have the culprit. You do not have to open up housings and expose electrical contacts. You are looking at where your hand is, not where the meter is. Most people are capable of doing repairs and will get it going and not get hurt if they use a little sense. The voltage detector makes it even easier.
    GWolff's Avatar
    GWolff Posts: 2, Reputation: 1
    New Member
     
    #4

    Dec 31, 2007, 03:28 PM
    Update on this problem. The blower motor was cooked. I replaced it and the air handler now works fine. The Heat Pump still attempts to start when I reset the breaker, and then it eventually trips the heat pump CB. We determined that the compressor is internally shorted to ground, and it is history.
    Since it is winter in Florida... I don't need the AC, but I occasionally need some heat on a chilly morning.. (50 is cold down here ;) The airhandle has heat strips, so I still have a very primitive heat system for now. Time to save some cash to replace a tired and old system. Thanks for the troubleshooting help.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Air handler [ 4 Answers ]

My, carrier indoor air handler keep shorting out low voltage transformers. I've replaced 2 of them, the system will run for about 5 hrs. before it shorts out. ...

Air Handler [ 1 Answers ]

I live in Fl and my heat pump is outside and the air handler is in the attic. I discovered the tray under the air handler was overflowing and used a wet vac to remove it. My ceiling is getting wetter and wetter in an area about 1x2 feet. I've removed the insulation where the water is and can't...

Air handler [ 1 Answers ]

I have a heat pump. When the air conditioner comes on it sounds normal then after a few seconds I hear like a swooshing noise coming from the air handler in the attic. It makes the noise then stops then few seconds later does it again.and keeps doing that every time.We had to have freon put in the...

Air handler [ 4 Answers ]

Our home inspection for the sale of our home specifies that "there is a small amount of growth starting on the paper located on the motor. Seller shall clean the paper and treat the unit with an anti microbial agent." Please tell me how to get into the air handler, and with what anti microbial...

Trane A/C Handler [ 2 Answers ]

The blower makes a slight noise, almost rattling. I looked at the blower unit and it has the part number M412TB31V. Now I'm not sure if that's just the wheel, motor or both the motor and wheel. I would like to replace the motor and wheel, as I can't determine exactly where the noise is coming...


View more questions Search