    Intermittant oil burner not starting
    Hi, I have a dual energy hot water furnace. When the temperature goes below -12°C, the oil furnace is supposed to start. 90% of the time it works. We have had 3 different technicians during the last 3-4 years. They have changed filters, nozzles, oil ignition control box, they have cleaned the electrodes and adjusted the mixture.
    My question is could it be a problem with the transformer not producing enough voltage? And is there a test for this?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 16, 2007, 12:02 PM
    Transformer about 10,000 volts. There is a special high voltage probe to test that hi a voltage. OR option B is to space a screw driver grounded to one transformer contact about 1/4 of a inch away from the other contact and see how far a arc you can pull when you move the screw driver back away from the other contact point. You need a nice hard blue arc about 1/2 inch minimum in length. The longer the better.

    The last way to test is really not that good but back in the 50's and 60's we did not have all the fancy tools of today to work with. If you really want to be accurate have the service tech use the high voltage probe. That is what the probe is designed for.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Honda del sol 95 intermittant start [ 3 Answers ]

Hello there, I have a 95 Honda del sol. The car starts and runs smoothly 98 % of times but sometimes in the morning it is starting to give me "no start". It used to be only cold and we weather symptom but this summer it gave me trouble twice. Important things I have noticed is that I need to press...

Intermittant Power [ 3 Answers ]

The air handler comes on as does the compressor and the thermostat has a reading. Then in 5-10 minuted there is a power loss to the indoor unit and the thermostat goes blank and the outdoor unit shuts down, then it everything comes back on and the whole thing happens again. I checked the...

Intermittant furnace shut down [ 1 Answers ]

I have a 15 year old Bryant gas forced air furnace. The furnace has shut down intermitantly this season. It has an electronic ignition that locks out and the furnace shuts down. When I flip the power switch off and on the spark will start and the furnace will operate again for days. Any...

Intermittant pilot ignition question [ 3 Answers ]

Hello, I have a problem with the intermittant pilot on my ~9 year old gas fired boiler that came with my house. It is a Vaillant boiler #GA92-120PV, with a honeywell gas valve #VR8204A, a Honeywell spark ignition control box #S8600F, and power vent. The boiler is at 8500 feet elevation, and has a...


View more questions Search