Senior Member
|
|
Dec 12, 2007, 05:29 PM
|
|
full load Current
Anybody want to take a crack at this?
What is the flc of a motor with a nameplate rating:
-1 ph
-240v
-Fla=16.5
- 3 hp
|
|
 |
Uber Member
|
|
Dec 12, 2007, 05:35 PM
|
|
If you mean for branch circuit wiring and device and OCPD sizing, then must use Table 430.148 rating of 17 amps.
For overload protection devices then use the nameplate rating of FLA 16.5 amps.
|
|
 |
Senior Member
|
|
Dec 12, 2007, 06:35 PM
|
|
I guess I'm bored!
Am I violating site rules :)
Any how, is that your last and final answer (any one accept TK)? ;)
|
|
 |
Home Repair & Remodeling Expert
|
|
Dec 12, 2007, 06:45 PM
|
|
None of us should get any closer to this one. No one except Kevin can answer this.
|
|
 |
Senior Member
|
|
Dec 12, 2007, 07:47 PM
|
|
If you mean for branch circuit wiring and device and OCPD sizing
Branch circuit conductor-->Sure do!
|
|
 |
Senior Member
|
|
Dec 12, 2007, 10:37 PM
|
|
Outside of the above being a requiremnt of 21.25A min requirement-- (17)(1.25%)
Tk,
If this unit was located in an environment, where it was considered continuous. Have you noticed anything in the NEC that says we would have to multiple an additional 1.25%?
|
|
 |
Uber Member
|
|
Dec 13, 2007, 04:04 AM
|
|
No, this 17 * 1.25 would be continuous rating and set the minimum rating of a OCPD. But depending on the type of OCPD and motor, refer to Table 430.52 for max ratings. Some of them may be surprising.
For example, a single phase motor and an instantaneous CB the max rating is 800%!
|
|
 |
Senior Member
|
|
Dec 13, 2007, 01:00 PM
|
|
Exactly! Excellent feed back!
|
|
 |
Uber Member
|
|
Dec 13, 2007, 02:00 PM
|
|
Ok, so your bored huh?
I have one for you.
Size the disconnect, branch circuit conductors, and overload devices, for a 25 HP 480 volt 3 phase fire pump.
Key word is "fire pump".
This ought to blow some minds
|
|
 |
Senior Member
|
|
Dec 13, 2007, 08:31 PM
|
|
Wow!
Talk about a confusing section. Seeing that this is something I will never install, I have an excuse for lack of knowledge. :) Yet, here it goes:
Based on the information:
-Conductor size=#8 CU per T.310.16 and T.430.250 (34)(125%)=42.5A >assuming a 75 degee termination<Also See 695.6(c)(2) <-assuming no VD
-Overload Protection=None required per NEC 695.6(d)--yet short circuit protection required for branch and feeders. Based on the information you provided. A 25HP 480v 3 ph max lock-rotor current disconnect=365 amps per 430.257(b)---so 400amps per 240.6
:) or :(
|
|
 |
Uber Member
|
|
Dec 14, 2007, 01:44 AM
|
|
So your saying a #8 wire on a 400 amp breaker and disconnect?
Sounds right to me.
|
|
 |
Senior Member
|
|
Dec 14, 2007, 09:28 AM
|
|
Where is my prize?
I'm sure this will have some people wondering... :)
Good question!
|
|
 |
Uber Member
|
|
Dec 14, 2007, 03:43 PM
|
|
Here you go...
I am surprised I did not get any comments about a #8 wire on a 400 amp breaker.
|
|
 |
Senior Member
|
|
Dec 14, 2007, 03:58 PM
|
|
I am surprised I did not get any comments about a #8 wire on a 400 amp breaker.
I was surprised as well. I was waiting on someone to ask how this was allowed. I guess they are out shopping or don't care! :)
|
|
 |
Junior Member
|
|
Dec 15, 2007, 08:39 AM
|
|
I know better than to question either of you! And I also know there are some strange exceptions out there for things like you exampled. So... in this case... even though I don't understand completely why it is what it is, I accept your answer!
Now... tell us why! A good teacher teaches... they just don't give tests! :)
|
|
 |
Uber Member
|
|
Dec 15, 2007, 09:24 AM
|
|
This is no test, just a discussion between a couple of tradesmen, one that may not have had a need to look for this situation. Better to be aware of something now to be prepared in the future if this situation ever arises.
Washington did well, hit the nail.
And to illustrate that there are exceptions, albeit, this is probably one of the most extreme.
A fire pump is a critical unit needed for several reasons, usually when there is not enough pressure or capacity in the normal water system to provide both to fill a sprinkler system, and to continue supplying water at the point of combustion.
Even thou there is mandatory testing and maintenance performed on the pump and system, it has been determined that due to Murphy's Law, the damn thing may have a problem at the time of a fire.
So provisions are in place to allow the motor to start, or allow it to try to start, and keep running, at any cost.
So all breakers, fuses, switching, transformers, etc, must be sized to handle the locked rotor amps of that motor. As you can see from the example, a 25 HP motor will have 365 amps of locked rotor current. The distribution system will be sized to handle this current.
The wire, while small to handle the normal starting and running current, is known to handle high current for a short period, and is consumable, is only sized to be 125% of the running current.
It is not practical to size wire to handle the LRA, so FLA is used.
If the pump has a problem, this will allow the pump to run, at any cost, even if it burns up. Suppressing the fire is the goal.
|
|
 |
Senior Member
|
|
Dec 15, 2007, 10:06 AM
|
|
 Originally Posted by tkrussell
This is no test, just a discussion between a couple of tradesmen, one that may not have had a need to look for this situation. Better to be aware of something now to be prepared in the future if this situation ever arises.
Washington did well, hit the nail.
And to illustrate that there are exceptions, albeit, this is probably one of the most extreme.
A fire pump is a critical unit needed for several reasons, usually when there is not enough pressure or capacity in the normal water system to provide both to fill a sprinkler system, and to continue supplying water at the point of combustion.
Even thou there is mandatory testing and maintenance performed on the pump and system, it has been determined that due to Murphy's Law, the damn thing may have a problem at the time of a fire.
So provisions are in place to allow the motor to start, or allow it to try to start, and keep running, at any cost.
So all breakers, fuses, switching, transformers, etc, must be sized to handle the locked rotor amps of that motor. As you can see from the example, a 25 HP motor will have 365 amps of locked rotor current. The distribution system will be sized to handle this current.
The wire, while small to handle the normal starting and running current, is known to handle high current for a short period of time, and is consumable, is only sized to be 125% of the running current.
It is not practical to size wire to handle the LRA, so FLA is used.
If the pump has a problem, this will allow the pump to run, at any cost, even if it burns up. Suppressing the fire is the goal.
Couldn't have said it better!
|
|
 |
Junior Member
|
|
Dec 16, 2007, 08:16 AM
|
|
And it makes perfect sense to me. Thanks guys!
|
|
 |
Senior Member
|
|
Dec 16, 2007, 01:34 PM
|
|
Ok, I just proof read my answer and found a mistake (typo) :(
It's actually 183A, and not 400A:(
Yet, still amazing! :)
|
|
 |
Uber Member
|
|
Dec 16, 2007, 01:53 PM
|
|
Damn, I did not double check that number, but still the answer is amazing.
Again, knowing the code can be your friend. I have met electricians that use wire rated full boat. What a waste of copper and labor, and money.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Current ratio and non current assets
[ 1 Answers ]
How do I know what each makes contains.
current assets 25,000
liabilities 40,000
equity 55,000
non current assets=80,000 ( Is this correct)
non current 60,000
Electrical current load
[ 2 Answers ]
Hi all,
My name is Jack from lockport, IL. I am installing a bathroom in my basement which include a sewage waste pump. The pump is 1/2 horse and rated at 19.4 amps normal running. Would it be too much if I was to hook the sewage pump, a gfci outlet (for shaver or hair dryer) two lights...
Which is better settle in full or paid in full
[ 20 Answers ]
I had a discover card opened when I was a young adult with my father(about eight years ago). As of a 18 months ago he stop paying on it even though the charges were made by him. Now I'm trying to take a step towards business ventures and this and some other things are on my credit are present. I...
View more questions
Search
|