Max Circuits in a Sub Panel
I have a 100A sub panel in my attached garage that is fed with 6/3 (copper NM-B) off a 40A breaker in my main panel. The panel has 6 slots and will handle 12 circuits. Now, my understanding is as long as I don't have more than 6 circuits on this sub panel, I am not required to run the feed through a main breaker at the panel. It doesn't have provisions for a main, so it would have to be back fed. I currently have two 240V 20A circuits and two 120V 20A circuits. That's a total of 6 breakers, but since I'm using combo breakers, it's only in 4 slots. I would like to add a couple of more circuits. My interpretation of the NEC says I can do this without needing a disconnect (main) at the sub panel as long as the total number of breakers in the panel only require 6 hand movements to shut down the entire panel. Correct or wrong? In other words... since my two 240V circuits are on tied breakers, they only count as one because the circuit can be shut off with one hand stroke. Please enlighten me if I'm wrong...
|
|
 |
Uber Member
|
|
Dec 7, 2007, 08:18 AM
|
|
Where in the code do you find " sub panel "?
The Six Switch Rule is for the Main Service Disconnecting Means. In otherwords, instead of having one breaker as the Main to shut down a service to a building, no more than six switches or breakers will suffice.
This is not necessary for a "subpanel", which would have a branch circuit breaker that protects the feeder to a subpanel.
A "subpanel" is nothing more than another circuit or feeder fed by the Main service.
So, you have all 12 circuits in the panel available for use.
|
|
 |
Junior Member
|
|
Dec 7, 2007, 09:40 AM
|
|
Thank you TK. I figured a panel was a panel was a panel. I also had a knowledgeable person tell me that my sub needed a main if I went over the six breakers. I agree with the way you read the rule now that you've explained it.
|
|
 |
New Member
|
|
Dec 8, 2007, 10:50 PM
|
|
TK - since we're on the subject :)
I was at home depot today - guy in elec dept (says he an electrician)
Says in my planned subpanel that since I will have 10 circuits,
I will need a main breaker in the subpanel (I just wanted to use an easier/
Cheaper main lug). I'm in Connecticut - he says CT inspectors consider a
Subpanel greater thatn 6 circuits to be its own main panel, so I need
A main breaker at the subpanel. Is this guy off? I see you are in new england -
Are you in CT?
|
|
 |
Senior Member
|
|
Dec 9, 2007, 03:57 AM
|
|
This is not necessary for a "subpanel", which would have a branch circuit breaker that protects the feeder to a subpanel.
TK, what about Article 225.33--which reference 225.30?
It is my understanding that if the feeder is suppling a panel on a remote structure, then you either need a main breaker panel as your disconnect (best), or settle for up to 6 grouped disconnects?
|
|
 |
Uber Member
|
|
Dec 9, 2007, 06:22 AM
|
|
Washington, for a remote building, yes, you are correct, per 225.33, a main or no more that six switches is needed at a remote building.
225.30 calls for the ONE OCPD to protect the remote building for the only one supply that is allowed, and must be on the load side of the service disconnecting means on that property,at the main service, and then lists conditions for more than one service if needed to the remote building.
Neither applies for this attached garage.
Grjack, without going into too much personal detail, just let me say I am more than a little familiar with Ct. However, while the clerk may have good advice, best to check with the actual local inspector for your town.
Never use any advice from a store clerk without confirming with an inspector or contractor, unless that clerk can provide a license for that trade.
All of Ct larger cities and towns have their own electrical inspector, I had met many of them, all gentlemen, may I say. One has a saying on his wall, "Arguing with an inspector is like wrestling with a hog in the mud, after a while you realize the hog loves it." He is my favorite.
Many of the smaller towns and villages will use a building inspector that is somewhat knowledgeable of electric, or borrow the services of a neighboring city inspector. Seldom do any use the State Inspector, that I know of. Here is where you may have interpretation issues, with the "fill in" inspectors. Talk to them, they will bend with reason, logic, and discussion of that particular code question.
If your panel is in the building that has the main service, then no main is required by NEC. If a detached building, then yes, one main or no more than six switches. Each local inspector may have their own requirements.
|
|
 |
Senior Member
|
|
Dec 9, 2007, 10:06 AM
|
|
Grjack
Got me off track.
Never use any advice from a store clerk
This is a #1 rule! :)
|
|
 |
New Member
|
|
Dec 10, 2007, 07:01 AM
|
|
Tk -
Thanks - since this is a remote barn, I'll use a main brker sub panel.
|
|
 |
Senior Member
|
|
Dec 10, 2007, 01:21 PM
|
|
 Originally Posted by grjack
tk -
thanks - since this is a remote barn, i'll use a main brker sub panel.
I'm with TK on starting your own question on a new message board.
Cobra,
Sorry for getting off track! I was so focused on grjack's question, that I though TK was wrong.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Determining capacity and maximum circuits in panel
[ 1 Answers ]
I can't find this info anywhere. I can only assume it's a dumb question.
When I look at my 100 amp panel I see 32 spots for breakers. Down one side I count 16 and another 16 on the other. There are two 30 amp and 1 60 amp, and then about 20 more 20 amp breakers. When I add it up I get 510 amps....
Adding Sub-panel and moving existing circuits to it.
[ 1 Answers ]
I'm looking at getting some tools that will require having 220 for them. My main panel is full right now and has several Slim/Tandem/double breakers in it already. Reading some things on the net I see that the panel might be exceeding the limit it should have for breakers, but don't know at this...
Kenmore Elite Dryer Toe panel - how to get panel OFF!
[ 3 Answers ]
I have a Kenmore Elite Model # 110.600094990 27 inch Electric Dryer - NOW How the heck does one take the Toe Panel Off / or Open this lower section of the dryer? There are two lower edge clips and two upper edge retainers. I CAN NOT get the panel to budge! This is a 7 yr old unit. Thx DAS
Sub panel circuits
[ 1 Answers ]
I Want to replace an existing unused 20 amp two phase electrical outlet with a sub-panel containing single phase 110 volt circuits with appropriate circuit breakers. My question is: How many separate circuits does the NEC allow in this type of sub-panel?
Sub panel fed with two circuits
[ 3 Answers ]
I was looking for space to add a circuit to an existing sub panel at my mother's house and ran into a problem that I need some advice on. Upon opening the sub panel, I discovered that it is being fed with two 12-3 Romex wires originating from two 20A circuits at the main. Now, I think that I...
View more questions
Search
|