    Furnace fan controler testing
    I have a fan controler with high temp shut off.is there a way to test the fan controler while not on the burner?
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Nov 20, 2007, 06:39 PM
    If it's a combination fan limit control with two wires on the left marked fan and two on the right marked limit. The line side wire on the switch will be hot all the time when the heat rises it closes the witch and gives power to the load side, if the blower fails to come on or doesn't move enough air it will open the limit side to kill 24v going to the gas valve. The easiest way is to turn your heat on and see if you get power to the load side when it reaches its fan on temp.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Nov 20, 2007, 06:40 PM
    Not really a safe way. You can rotate the control by hand to see if the safety kills power to the burner BUT you take a chance on causing the control to be out of calibration. They are not designed to be turned by hand.

    If you have a fix disc type you might be able to heat it and cause it to trip but unless it has a little red reset button chances are you will damage it because sometimes the non push button type will not reset on there own and then you will have to but a new one.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a furnace thermostat to manually operate the furnace fan [ 2 Answers ]

I have two wires connected to my furnace thermostat. There is a place labeled G on the thermostat. Can I simply run a wire from the G terminal on my thermostat to the terminal labeled G on my furnace fan relay to operate the fan separately?

Heil Fan Controler Buzz / Hum [ 3 Answers ]

Is it normal for a fan controler to have a Humm that you can notice when the fan Is running or not ? 2 Year old Heil gas unit.

Condenser Fan wiring and testing [ 8 Answers ]

Hi all. After two days of reading posts here off and on, I am have a much better understanding and much more conversant on this topic (all the better for the readers):D The condenser fan on my Haier 2 ton AC is not running. What I know: The compressor runs fine There is 220 at the...

Comfortmaker Furnace Fan blows in line fuse and will not allow furnace to work [ 1 Answers ]

I have a Comfortmaker Furnace (approximately 1998/99) and the fan will not turn on allow the furnace to heat. When I try to turn the furnace on it blows a 3 amp fuse at the blower motor. I removed the fuse and jumped it and all it will do is make a faint buzzing noise and not turn on. I can...


View more questions Search