    Sub panel ?
    Hi:

    After a main service disconnect the electrical panel located 80' away is considered as a sub-panel ?

    Thanks
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Nov 19, 2007, 05:55 AM
    Does that panel have the neutral bus separated from the ground bus?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Nov 19, 2007, 06:46 AM
    They should be separated in a sub panel, that doesn't mean it is a sub panel.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 19, 2007, 12:40 PM
    For the purpose of your question, which I will assume is regarding grounding, and the separation of the neutral and equipment ground beyond the Service Disconnecting Means, yes, the Main panel will be connected the same as a "subpanel", as being a sub, or below, or beyond, the Main.

    Keep in mind, there is no technical term "subpanel" listed, defined, or used in the actual National Electric Code text. This is a trade term created by electricians to indicate a panelboard that does not contain the Main Service Disconnecting Means.

    We know that the grounding of the neutral and bonding to the equipment grounding conductor happens at or before the Main.

    We all know what each other is talking about, and have tended to "create" abbreviations and/or slang for terms, equipment, etc. These terms then get out to laypeople, who at times, may used them in the wrong context.

    So, if you are referring to your "main" panel as a "subpanel", in the context that the neutral must be insulated and isolated from any equipment ground, then you are correct in your thinking.
    Henry-fla's Avatar
    Henry-fla Posts: 2, Reputation: 1
    New Member
     
    #5

    Nov 20, 2007, 05:49 AM
    Thank tkrussell , that is exactly the picture.

    Now, I'm planning to run 3 # 1/0 XHHW,AL, and 1 # 6 THHN, CU on 125 amp, 240 v service, through a 1 1/2 PVC SCH 40 attached along the wall from 125 amp main disconnect to 125 amp main lug panel. Is anything wrong with this on commercial work ?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Nov 20, 2007, 11:38 AM
    #1/0 Al is only good for 120 amps, using the 75Deg C column of table 310.16 of the NEC, so need to use #2/0 Al for a 125 amp feeder.

    The 1.5" PVc Sch 40 can handle 4-#2/0 XHHW Al, so the conduit size is good.

    Assuming the conduit run will be horizontal on the exterior of the building, expansion couplings will be needed, due to the expansion of PVC, esp in areas the outdoor temp gets hot.

    Review:http://www.carlon.com/Installation_T...-NEMAEXJTA.pdf

    This info is also found in Article 352 Nonmetallic Conduit, along with supporting interval of every 5 feet for 1.5" PVC conduit.

    I assure you, strapping even at every five feet, the conduit will sag between supports and end up looking like a roller coaster. While horizontal runs are allowed, most good electricians will not run PVC any great lengths horizontally, as there will be complaints of the appearance.

    The choice is yours, as long as you heed the warning.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Breaker size in main panel to support sub panel? [ 7 Answers ]

Hello, I am wiring a sub-panel to the outside of my home (50 feet from main 200 amp box). I ran 3 wire - 6 gauge. What is the largest 2 pole breaker I can put in the main panel to supply the sub-panel. TYPE NM-B 6-3 WITH GROUND 600 VOLTS CIRTEX-I EZ-STRIP (R) PLUS 17:11 2/5/07 SB/RC ...

Connecting main panel to sub-panel? [ 1 Answers ]

I have my sub-panel for my workshop all set up, plugs & lites all wired in. The workshop isn't attached to the house & I was wondering what the best way was to connect from the main panel in the house to the sub-panel in the workshop?

200 AMP Service panel to 200Amp Sub Panel [ 1 Answers ]

I getting new 200Amp service to surface mount service panel. I want to run 2oo cable to bring it sub panel in my Garage which is approx 120Ft Run through ceiling. 2 Questions 1. Is there any ristriction on running a 200AMP inside house to garage ? 2. I got a dirt cheap subpanel that has...

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...

Kenmore Elite Dryer Toe panel - how to get panel OFF! [ 3 Answers ]

I have a Kenmore Elite Model # 110.600094990 27 inch Electric Dryer - NOW How the heck does one take the Toe Panel Off / or Open this lower section of the dryer? There are two lower edge clips and two upper edge retainers. I CAN NOT get the panel to budge! This is a 7 yr old unit. Thx DAS


View more questions Search