Hello I have a new Goodman 90% efficiency furnace. The induction motor keeps getting water in it and then the pressure switch trips. The drain is not plugged and is flowing good. Any help would be appreciated. Thanks Dan
|
|
 |
Heating & Air Conditioning Expert
|
|
Nov 15, 2007, 10:55 PM
|
|
Check drain and blow clear. Next make sure the drain has a trap in it.
Next question. Did this just start doing this? How long have you had the furnace?
|
|
 |
New Member
|
|
Nov 16, 2007, 06:16 AM
|
|
This is the first time I used the furnace , it is a new house. My furnace guy says he has never seen a furnace do this. The drain appears to be flowing a good amount of water out of it. The induction motor exits on the right upper side of the furnace. Where the pipe makes a 90 uppwards, there is a drain tube at the bottom of that 90. The drain tube then drains over to the side of the furnace into a small plastic box (trap). When that fills up, the water then flows into 1/2 inch plastic into the floor drain.
|
|
 |
Uber Member
|
|
Nov 16, 2007, 08:23 AM
|
|
What about the length, diameter and number of elbows in the intake and exhaust?
|
|
 |
Home Repair & Remodeling Expert
|
|
Nov 16, 2007, 09:15 AM
|
|
"This is the first time I used the furnace , it is a new house" so why are you trying to find the fix? The builder and his HVAC sub should be working on this to your satisfaction. How long is your new home warranty? It sounds like new installation that could be faulty or the equipment may be faulty but in any case you do not have to worry about the repair. Exercise your rights.
|
|
 |
Junior Member
|
|
Nov 16, 2007, 12:07 PM
|
|
Your problem can only be caused by the following 2 issues... 1. if you tell us that the vent pipe is draining OK from the inducer, then the only other point that is NOT draining is the condensate from the furnace collector box that the forced draft inducer is attached to. This collector box collects condensation from the secondary heat exchanger and must also drain! If it does not, the water level will rise until it flows into the inducer and slows down the fan... and the pressure switch will not make. Look for a lower hose from the collector and check there as to why it is NOT draining. NOTE: you will have to take the inducer off to empty it of water...
|
|
 |
Junior Member
|
|
Nov 16, 2007, 12:10 PM
|
|
Another point to check is ALL of these drain hoses for PVC chips from cutting the exhaust pipe... is not blocking the proper water drainage out of the unit...
|
|
 |
Home Repair & Remodeling Expert
|
|
Nov 16, 2007, 03:09 PM
|
|
You have gotten some very good advice from several people who know what they say. However, I am still taking the point that you should not do anything at all. New house, new furnace, home warranty, first use... call the contractor or his sub, period. I doubt that you could do anything to void your warranty but why take the chance, exercise the warranty instead.
|
|
 |
Junior Member
|
|
Nov 16, 2007, 04:45 PM
|
|
tsa7man is correct as I have seen this happen personally. So is ballengerb1 which is the route I'd persure if it was my new home...
|
|
 |
Junior Member
|
|
Nov 16, 2007, 07:00 PM
|
|
WELL WE ALL GAVE YOU WAYS TO SOLVE YOUR PROBLEM... that is what this web site is all about... the best is the new warranty / new home issue... take your pick, if it was me, go with the new home... let them fix the problem!! GOOD LUCK... tsa7man
|
|
 |
Ultra Member
|
|
Nov 16, 2007, 07:18 PM
|
|
If it's a new furnace make sure the system has been converted for its use. Horizontal left use different drains than horizontal right along with up flow or down flow systems. Most systems come set up for up flow and have to be converted for any other position. If just one hose was not moved for its application it will not drain.
|
|
 |
New Member
|
|
Oct 16, 2011, 09:55 AM
|
|
I has the same problem with my Furnace(Miler G6RC). Water would fill up the inducer and pressure switch would be stuck open. It would not reach the set temp. on the thermostat either. When I drain the water; furnace would run an OK cycle but same thing would happen for the next cycle. After draining it so many times I found out that the tube was obviously filled with gunk. Cleaned that out and it seems to be running awesome. And also running up to the set temperature. Hopefully it will help you too and not have to spend hard earned money on the call
|
|
 |
New Member
|
|
Nov 23, 2011, 07:54 AM
|
|
I had same issue... check for LEVEL on your furnace. If not level, water stays in fan and motor can not make enough vacuum to close the switch.
|
|
 |
New Member
|
|
Jan 10, 2014, 06:57 AM
|
|
I am having a similar problem with my Goodman furnace. Water collects in the blower motor chamber when it rains. The condenser is bone dry and there is not a single drop of water exiting the system from there. Please help... any advice would be greatly appreciated!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Furnace blower motor
[ 10 Answers ]
I have a Climatrol Furnace, and it stopped working. I called a Heating Co, and the technician said that that the motor was bad, it's and old unit with Climatrol no longer in business. I might be able to find a used motor, but I really need a new furnace.
After he left I was reaching in and I was...
Furnace inducer motor
[ 5 Answers ]
What are the implications of a furnace inducer motor drawing high Amps?
Induction motor
[ 1 Answers ]
How do we reverse the direction of rotation of a induction motor?along with circuit diagram.
Reversing induction motor direction
[ 0 Answers ]
How can be the direction of rotation of an induction motor reversed apart from reversing the connections of condensor(capacitor in table fan) ?
Furnace Blower Motor
[ 8 Answers ]
I am replacing my blower motor. My question is when replacing it do I have to get exactly what the label has on it because I'm having trouble finding the exact numbers online? I am looking for 4HP, 115V, 60HZ, 6.3A, 1050/850RPM. It was made by Franklin Electric unfortunately it looks like they...
View more questions
Search
|