    #1

    Nov 12, 2007, 06:51 AM
    15 amp GFCI breaker popping
    Hi, I have a GFCI breaker that pops when we vacuum in any room in the back of the house. Since we could be using 4 different plugs that pop the same breaker, would you start with the breaker? Also, would it be unwise to go to a 20 amp GFCI breaker :eek: ? Thanks Scott
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 12, 2007, 07:07 AM
    You can only change the breaker to a 20 amp if the entire circuit is #12 copper wiring.

    The 15 amp GFI breaker may be defective, or there may be an overload on the circuit with the vacuum.

    Only measuring the amperes on the circuit will help pin this down. Just replacing the breaker with a new one may not solve the problem.
    trishandscott's Avatar
    trishandscott Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 14, 2007, 06:30 AM
    To measure the amps do I just put a meter on the different plugs in the house or on the breaker? Thanks
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Nov 14, 2007, 08:16 AM
    The easiest way is with a clamp on meter such as this one. Ideal 61-701 Clamp Meter, 200AMP, Ideal 701, 61-701, 61701

    This Extech Instruments: Clamp-on Meters: Accessories: 480172 allows you to measure an existing appliance with the above meter.

    For these meters to work, one side of the line (one of the wires L or N) must go through the clamp.

    The clamp meter can also be used at the breaker box without the adapter.

    The "adapter" can be made from a few short lengths of wire, a plug and a female cord connector.

    The other way is to use the ammeter function of a multimeter.

    A real simple solution might be this: Ross Olson's Order Somewhere Chaos + Kill A Watt Home Wattage Meter

    A meter such as this one: http://www.groundtesterstore.com/crm...ds/2117.56.pdf

    ~$270 can evaluate both the leakage currents which would trip the GFCI and the load current.

    As with all test equipment, you need to know how to use them properly. Your trying to identify which part is bad: GFCI, house Wiring, vacuum wiring, vacuum overload or breaker.

    With the proper tools you can identify the problem with proper measurements. Amp draw of the vacuum and leakage current of the vacuum. With this you can eliminate the vacuum.

    Measuring the current at the breaker, you can eliminate the breaker. The breaker must carry the vacuum + any static load.

    Wall wiring typically doesn't go bad, so you'd replace the breaker.

    So each tool I suggested either allows you to get to part, but not all of the problem except one meter. Even the Kill A watt can only determine if the vacuum is malfunctioning. It can't easily tell you if the circuit is overloaded.

    There are ways to measure leakage currents without all of the fancy meters, but I forget from my electronics servicing days. I think it was something like measuring the voltage drop across a 10K resistor from ground to any exposed metal parts when the ground connection was removed and converting that to a current.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Hot Tub and using a 50 Amp Double Pole GFCI Circiut Breaker [ 10 Answers ]

:confused: I keep getting the GFCI breaker tripping after wiring my hot tub. I wired 2 hot Red and Black to the proper terminals and the White to the neutral and the Bare Copper to the ground Post at the tub. I am using 6-3 w/G per instructions. Could the GFCI breaker be bad? When I wire...

Replacing GFCI Breaker With A Regular Breaker [ 1 Answers ]

I have a 15 amp circuit serving only a single outlet on my deck. It is protected by a GFCI circuit breaker in the home's single 125 amp service panel. I wish to replace the GFCI breaker with a regular 15 amp GE breaker. I will then protect the circuit with a GFCI outlet. I am familiar with...

Gfci popping now? [ 5 Answers ]

OK I have a fridge and a freezer in basement plugged into an outlet that's connected to a 20 amp gfci receptacle in the garage wired to a 15 amp breaker in fuse panel. It's been this way for 15 years without problem.. Now gfci pops. I unplugged the freezer (about 5 years old) and everything works...

GFCI rapid popping [ 3 Answers ]

While using my hair dryer this morning, it lost power and the GFCI outlet on the circuit started making a repetitive popping noise. I unplugged the razor charger on the GFCI outlet as well as the hair dryer and electric toothbrush on the non-GFCI outlet. I pressed reset, then test, then reset. ...

Gfci breaker popping [ 8 Answers ]

After installing a second outdoor fan, I tied into an existing fan under an enclosed porch.I decided it would be smart to install a gfci breaker to protect them (vs the standard breaker). The circuit is tied into my kitchen an outdoor spot lights. With all the individual light circuits either...


View more questions Search