    muhdavj's Avatar
    muhdavj Posts: 3, Reputation: 1
    New Member
     
    #1

    Nov 13, 2007, 09:14 AM
    2" vs 3" exhaust vent
    Should have read the manual - 90% Heil furnace, 100K BTUs calls for 3" PVC pipe. Allows 5 elbows (90s) & a 40' run. I have 2" PVC with only two 90s (sweep) & one 22.5 with a 15' run. Furnace is running well but I should probably change out the vent pipe. Any advice? - Dave
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Nov 13, 2007, 09:38 AM
    Yes, change the pipe to meet the manufacturers spec. Many high efficient furnaces now use a 4" PVC. You must have installed a reducer and that is where you should start with the replacement.
    muhdavj's Avatar
    muhdavj Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 13, 2007, 09:47 AM
    Quote Originally Posted by ballengerb1
    Yes, change the pipe to meet the manufacturers spec. Many high efficient furnaces now use a 4" PVC. You must have installed a reducer and that is where you should start with the replacement.
    Will do, although I didn't use a reducer, it was 2" out of the starting blocks. I'll add a 2" to 3" on the vertical right out of the housing and change out the pipe.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    Nov 13, 2007, 09:58 AM
    I don't know why some manufacturers do that but my Amana furnace comes out of the chamber as a 3" PVC but the specs then call for a 4" exhaust. I think that possibly if the exhaust is larger than the chamber it reduces pressue in the exhaust and makes the flow of exhaust move more easily.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Nov 13, 2007, 10:23 AM
    If you did the install and start up yourself, did you check the air flow? If you set the inducer speed high enough you may get away with restrictive vent.
    tsa7man's Avatar
    tsa7man Posts: 154, Reputation: 9
    Junior Member
     
    #6

    Nov 13, 2007, 07:46 PM
    There are a number of issues with a too small of a vent, where the factory spec. is 3 inches. As the inducer get old, it will not be able to pull in the pressure switch, and at this point, you may be on the very edge of the pressure switch making. By checking the rise through the furnace, you may find that it is on the high side... where it should by about 55 degree F difference with correct air flow through the heat exchanger and circulation blower on the proper tap. Another important issue is that you may not a long life out of the heat exchanger... it is best to change it to 3 inch, use an increaser close to the furnace. ( if this is a 2-pipe furnace... be sure to change both to 3 inch )
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #7

    Nov 14, 2007, 08:27 AM
    I think TSA did a good job of explaining the issue. I believe that your warranty would not be honored if you did not follow Heil's install instructions.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

A/C or Heat does not work w/thermostat set "on" or "auto". [ 22 Answers ]

A/C or Heat doesn't work in "on" or "auto". Fan will not come on at the "on" position either. I changed the batteries in the thermostat. I also read somewhere to disconnect the "Y" and hold it to the "R" on the thermostat for two minutes. That will tell me if the thermostat is the problem. ...

Proper venting & using a "Sure-Vent" [ 2 Answers ]

I've attached a PDF showing the layout I'm working with. The items in red are what I would like to add (for a new bar sink). From what I've read online and with checking with local plumbers and since I'm more than 3-1/2' from the main 2" drain line (and I'm using 1 1/2" pipe), I have to vent the...

Using "Studor" mini vent in bathroom wall [ 1 Answers ]

I am completely renovating a bathroom in a 1973 mobile home. There is no vent stack from any of the toilet, tub or lav fixtures. I plan to install the "Studor" vent in the wall. Can I use one vent for two fixtures or does each fixture need it's own vent?

Honda accord 2000 6 cyl " the light "check" is on" [ 1 Answers ]

My honda accord 2000 6 cyl. With 101000k miles is was with the light "check" on. I took To a non-honda mechanic and he erased it. The computer said that the code is PO700, and the mechanic said that it needs to have the "transmission rebuilt", and the price ranges from $ 1500.00 - 1600.00. My...

Can not "copy", "paste" and "cut" ! [ 2 Answers ]

Last week, my laptop was infected by virus, I sent for repair. After that, I couldn't find "copy" and "cut", and"paste" is in grey colour ! What have to do to have them back ? Can someone help ? Thanks in advance !


View more questions Search