    Hunter Thermostat
    Just got a Hunter Thermostat my old one s wires are R,G,Y,W,B. the new one is G,RC,RH,Y/O,W/B,Y1. How do you wire this one I wired it like the instruction and AC works but NO Heat?? Help
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #2

    Nov 6, 2007, 06:25 PM
    Is your system a heat pump system?
    houndoghank's Avatar
    houndoghank Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 6, 2007, 06:40 PM
    No its electric heat & AC
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Nov 6, 2007, 07:11 PM
    Do you have the red wire jumpered to both RC and RH? If you have the white wire on W/B, try it on Y1 or vice versa. While you have it off, try connecting the red and white wires. If the furnace doesn't start a heat cycle, the problem isn't at the thermostat.
    houndoghank's Avatar
    houndoghank Posts: 3, Reputation: 1
    New Member
     
    #5

    Nov 6, 2007, 07:32 PM
    The instructions say on 5 wires take the jumper off and red and white togeather does nothing, but it worked until I unhooked the other thermostat.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #6

    Nov 6, 2007, 08:51 PM
    Check your transfomer,, should have 24 volts coming out,, if not,, needs replacing,this is what gives you low voltage for the controls
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #7

    Nov 6, 2007, 09:24 PM
    The red should be hot from the transformer. If connecting it to the white didn't start a furnace cycle, something is wrong at the furnace, likely you have lost the control voltage. Newer furnaces have a fuse on the control board. If you need help locating it, see https://www.askmehelpdesk.com/heatin...ons-58313.html There is also a good explanation of thermostat wires. To get heat, you must have a hot wire from a transformer connected to RH. It can either be the same one as connected to RC, or another wire from a second transformer. Since the old thermostat didn't have RH & RC, the wire to B likely was a common some thermostats need for power. Check at the furnace and see if it is connected to com.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hunter Thermostat Wiring [ 8 Answers ]

It seems we are all having trouble with the Hunter 44110. I just moved into a house and I'm trying to install my programmable thermostat. I'm going from a Simple Comfort 2001 with a green, yellow, white, blue and red set up as G Y W C R I'm confused as do I use the jumper wire in Rh and...

Hunter Thermostat Wiring [ 11 Answers ]

I have an older Honeywell electromechanical programmable thermostat which I want to replace with a Hunter Model 44360 electronic programmable thermostat. I can figure out the "w", "g", "r" and "y" wires but I have a blue wire on terminal "c" and a brown wire on another terminal marked"c" on the...

Upgrading to a Hunter Thermostat [ 1 Answers ]

I'm upgrading from a Janitrol HPT 18-60 thermostat to a Hunter 44110 Thermostat. The wiring for the Janitrol is: Y = Yellow wire G = Green wire R = Red wire O = Orange wire W2 = White wire E = Black wire

Hunter thermostat 44110 [ 2 Answers ]

I have hot water baseboard heat, and installed the hunter digital thermostat 44110, and followed the directions as directed, I had had wires W, Y and RH, I marked and installed Each of the wires, and put them where they were marked on the thermostat. I felt well and all of the lights ( temp,...

Need Help with Hunter Thermostat Please [ 4 Answers ]

I have a Payne PF1MNC hvac, and just replaced my White Rodgers thermostat (It wasn't blowing hot air or kicking in in Auto mode) with a Hunter 44155C. There were 4 wires attached: G to G R to Rh (with jumper) Y to Y1 W to W And an unattached B I attached them the same to the Hunter:


View more questions Search