    Do I need a Studor Vent
    The contractor who is remodeling my kitchen installed a new sink. The drain pipe goes under the floor through the crawl space. He said there is enough height to the drainage, so there is no need to install a vent. I have read that you need to install a studor vent if it's hard to connect to the house main vent. Is the contractor correct?
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #2

    Oct 18, 2007, 04:18 AM
    Quote Originally Posted by Tiger20854
    The contractor who is remodeling my kitchen installed a new sink. The drain pipe goes under the floor through the crawl space. He said there is enough height to the drainage, so there is no need to install a vent. I have read that you need to install a studor vent if it's hard to connect to the house main vent. Is the contractor correct?
    Well, it needs some kind of vent -- And if venting through the roof or tying in to an existing vent stack isn't feasible, then it should have a Studor or Oatey AAV.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #3

    Oct 18, 2007, 06:04 AM
    The drain pipe goes under the floor through the crawl space. He said there is enough height to the drainage, so there is no need to install a vent.
    Your contractor has built you a illegal "S" trap. Chapter 14 Section 1409.2 of The Standard Plumbing Code tells me that each trapped fixture shall be vented. When you add that to Chapter 7,section 703.5 that prohibits "S" traps you have a contractor that should be sent back to plumbing school to learn basic plumbing 101. Since it's too late to add a outside vent a Studor vent's better then no vent at all. Good luck, Tom
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #4

    Oct 18, 2007, 06:26 AM
    Quote Originally Posted by speedball1
    Your contractor has built you a illegal "S" trap. Chapter 14 Section 1409.2 of The Standard Plumbing Code tells me that each trapped fixture shall be vented. When you add that to Chapter 7,section 703.5 that prohibits "S" traps you have a contractor that should be sent back to plumbing school to learn basic plumbing 101. Since it's too late to add a outside vent a Studor vent's better then no vent at all. Good luck, Tom
    It may or may not be an s-trap, Tom.

    Remember the guy from Canada several months ago who had the trap for his kitchen sink below the floor joists with the standpipe coming up through the bottom of the sink cabinet?

    It was a hokie set-up to be sure, but it wasn't an s-trap.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #5

    Oct 18, 2007, 06:53 AM
    It may or may not be an s-trap, Tom.
    Remember the guy from Canada several months ago who had the trap for his kitchen sink below the floor joists with the standpipe coming up through the bottom of the sink cabinet?
    It was a hokie set-up to be sure, but it wasn't an s-trap.
    You're stretching for this one groowler. There should be no good reason a plumber would increase the tail piece length to drop under the floor to a "P" trap when he could cut in a sanitary tee at the correct height. Hey! If it walks like a "S" trap and quacks like a "S" trap then that's the way I see it.
    Regards, Tom
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #6

    Oct 18, 2007, 07:02 AM
    If it is an ''S'' trap, I wonder if this guy follows the electrical code as closely as the plumbing code.
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #7

    Oct 19, 2007, 06:01 AM
    Quote Originally Posted by speedball1
    You're stretching for this one growler.
    No, I'm not -- Just because you've never seen it doesn't mean it isn't done.

    There should be no good reason a plumber would increase the tail piece length to drop under the floor to a "P" trap when he could cut in a sanitary tee at the correct height.
    There is if the practice is accepted by the local authority, as it was in this example.

    Look, neither you or myself would do such a thing, but that doesn't mean it isn't done and done in compliance with local code and the approval of the local authority.

    Get off your high horse and stop acting as though the code you learned is the only code in use.

    Hey! If it walks like a "S" trap and quacks like a "S" trap then that's the way I see it.
    Regards, Tom
    As you can see, the example I refer to above isn't an "S" trap.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #8

    Oct 19, 2007, 06:24 AM
    Quote Originally Posted by iamgrowler
    No, I'm not -- Just because you've never seen it doesn't mean it isn't done.



    There is if the practice is accepted by the local authority, as it was in this example.

    Look, neither you or myself would do such a thing, but that doesn't mean it isn't done and done in compliance with local code and the approval of the local authority.

    Get off your high horse and stop acting as though the code you learned is the only code in use.



    As you can see, the example I refer to above isn't an "S" trap.
    As I've stated, you're stretching for this one. It may be within code but it's not common practice.
    Of coures there are exceptions and of course it's done. And don't tell me that I'[ve never dropped a trap under the floor line. I remember having to trap a second floor shower that way. Back the hell off with the sarcastic remarks.
    Get off your high horse and stop acting as though the code you learned is the only code in use.
    I never said that picking up a trap with a extra long raiser was against code.
    The Op said the pipe ran down beneath the floor line. I repeat, " If it walks like a " If it walks like a " trap and quacks like a " trap and quacks like a " trap then that's the way I see it.. "
    Sure it could have a trap under the floor line but the OP described a " trap then that's the way I see it.." trap set up. So don't come in all rightious and belittle the obvious. Putting a trap under the floor when it belongs 18" above said floor is not usual plumbing practice so you climb down off your high horse. You're not the only plumber on this page with field experience. Having said that I consider you a competent mechanic who just comes off a bit huffy at times. Regards, Tom
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #9

    Oct 19, 2007, 06:56 AM
    Quote Originally Posted by speedball1
    As I've stated, you're stretching for this one.
    And I'm telling you, again, that I'm not.

    Furthermore -- I supported my position, which beats the heck out of anything you've had to say on the topic.

    It may be within code but it's not common practice.
    If it's within code, then how can it not be common practice?

    Fer crying out loud, Tom, how can you be this thick?

    Y'know, Tom, if you want to run this board as your own personal dictatorship -- Then have at it, just don't expect me to kiss your butt every time you fly off the handle.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #10

    Oct 19, 2007, 07:03 AM
    Go back and read my post again. You've missed the point. DROPPING A SINK TRAP BENEATH THE FLOOR LINE'S NOTCOMMON PRACTICE.
    And for petes sake, lose the attitude! Tom
    iamgrowler's Avatar
    iamgrowler Posts: 1,421, Reputation: 110
    Ultra Member
     
    #11

    Oct 19, 2007, 06:37 PM
    Quote Originally Posted by speedball1
    Go back and read my post again.
    Not only did I read and re-read it several times, I saved and archived it for the next time you so flippantly accuse me of "stretching it".

    I'm not just good at what I do, Tom, I'm *VERY* good.

    You've missed the point. DROPPING A SINK TRAP BENEATH THE FLOOR LINE'S NOTCOMMON PRACTICE.
    No, I didn't miss the point at all.

    I've said it before and I'll say it again -- Codes differ from locale to locale.

    If it is code in only one municipality, it is still common practice in that municipality.

    Period.

    Frankly, you need to get it through that thick skull of yours that what passes for code in your lil' fiefdom isn't necessarily what passes for code outside of your lil' fiefdom.

    Period.

    And for petes sake, lose the attitude!
    Fighting for what is right and pointing out that there is more ways than one to skin a cat isn't "attitude", Tom.

    Look, if you think my being an advocate for a differing point of view is about "attitude", then petition the moderators to ban my posts -- Otherwise, back the hell off.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #12

    Oct 20, 2007, 05:17 AM
    back the hell off.
    Nio! You back the hell off. Hey! You can install all the traps you wish with a 6' raiser if you believe it's "common practice".
    I've said it before and I'll say it again -- Codes differ from locale to locale.
    If it is code in only one municipality, it is still common practice in that municipality.
    Period.
    Frankly, you need to get it through that thick skull of yours that what passes for code in your lil' fiefdom isn't necessarily what passes for code outside of your lil' fiefdom.
    Talk about thick. How did code creep into this? I never said that a extra long raiser was against code. Hell! I've had to install one or two that way myself. What I said was a tailpiece that runs through the floor indicates a "S" trap and you jumped all over it like you were the only expert on this page with field experience. Get off your high horse and stop acting like your "The Defender of The Code". Of course I reealize codes differ from area to area. We have to license ourselves to work out on the each of the islands and keys that are off our coast. Don't tell me about different codes. Ban you? For what? Being pompous, opinionated and argumantative? Nah!
    I'll just let your attitude speak for itself.
    I'm not just good at what I do, Tom, I'm *VERY* good.
    On behalf of the other experts we feel honored to have such a humble man on tap to criticize and correct out posts. Here's a big hug to start your day! Let me end this post with a familiar refrain. "And for petes sake, lose the attitude!!"

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Studor Mini-Vent [ 5 Answers ]

I recently had my kitchen remodeled and the plumber installed a Studor Mini-Vent under the sink. Due to space limitations, he installed it sideways and didn't glue the PVC pipes together so it's easily removed. Is this a proper installation? I am pretty sure this (either the vent or the break in...

Venting sewage ejector w/ a studor vent [ 5 Answers ]

Hello, my home builder put drain pipes for tub, toilet and lavatory in basement floor; I'de like to know if venting my sewage ejector w/ a studor vent is up to plumbing code and if it will work for a full bath or must I dry vent it to the supplied vent in basement. Also, will venting the lavatory...

Studor Vent [ 1 Answers ]

I recently got a new roof (flat) after Hurricane Wilma. My bathroom vent pipe had blown out through the roof and the roofers stupidly tarred over the drain. Not wanting to open up the roof, the contracted plumber said that a studor vent could be used instead of opening up the hole on the roof. Even...

Studor Vent Failing? [ 3 Answers ]

We have a Studor Terminal in an inside hallway closet in our home. Occasionally, when you walk by you can smell the sewer gases, the nice rotten egg smell of hydrogen sulfide. I thought these were a one way air vent system and prevented this sort of thing? Is it not functioning properly?...

Studor vent with tow lavs [ 1 Answers ]

I have a 6 foot lav in my new addition. The bath is on the 2nd floor and there is no way to run the drain into the wall because of the joist below the wall. I am going through the floor into the 1st floor joist space with both lav drains. My question is -Can I use one studor vent for both lavs? I...


View more questions Search