    New 200 amp service
    What size cable would be needed to carry new service 530' to a 200 amp panel? Also does anyone know if schedule 40 can be place of 80 if the conduit is in a lawn with no driveway or walkway crossings? This would be in Franklinville, New York.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 4, 2007, 04:09 AM
    A 200 amp service can be loaded to 160 amps, 80%. Assuming this would be the max load, and assuming the voltage is 120/240, and keep the voltage drop at or below the recommended 3%, would require 500 MCM aluminum, for 2.5%, or 300 MCM copper for 3%.

    I don't even want to speculate what the copper would cost.

    This is an excessive length for 120/240 volts.

    Why is the run 530 feet? Is this because the utility transformer is so far way from the home? Is getting the utility closer an option?

    Schedule 40 is fine for normal soil conditions. Best to lay the conduit on a 6"bed of clean sand, and cover with 6" of sand, before backfilling with virgin soil.

    While 4" PVC would be the standard size for 500 MCM, with this length you may want to consider 5" or 6" PVC Sch40.
    fiedler98's Avatar
    fiedler98 Posts: 4, Reputation: 1
    New Member
     
    #3

    Oct 4, 2007, 11:42 AM
    The electric company here wanted over $7300. To get service closer. I told them to forget it and just get the service to my property line (hence the 530' distance). They did put a transformer on the pole and I am the only service from it. The house was planned to be a bit off the road. I have great friends that do excavating and construction work and it is amazing what they can do for beer and pizza.
    I've heard of copper coated aluminum - any opinion on that?
    Thank you for your help
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Oct 4, 2007, 11:52 AM
    That is only used for connection purposes. Still has the same ampacity as aluminum, so still need the same size, but more costly than plain aluminum.

    Look into you providing the high voltage line to a pad mount transformer, either provided by you or the utility, but much closer to the home.

    Still need trenching, and PVC conduit, and the wire will be much smaller, probably a #2 copper 5 Kv (kilo-volt)cable.

    Or you can get a price from a private pole line contractor to extend the pole line closer. You would own and maintain this pole line.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...

100 amp service vs. 200 amp service [ 5 Answers ]

The house I just bought was built in 1952. It's a 3 bedroom, 1 bathroom with the standard screw in fuses (total amps unknown). Presently I'm doing a remodel. Adding a third bedroom & extra bathroom, washer & dryer, dishwasher, newer & larger refrigerator, bigger microwwave, probably 3 window air...

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.


View more questions Search