Ask Experts Questions for FREE Help !
Ask
    nraschilla's Avatar
    nraschilla Posts: 1, Reputation: 1
    New Member
     
    #1

    Oct 2, 2007, 06:58 AM
    Additional 100 amp service
    I just finished a 24' X 30' pole building and want to install a 100 amp panel. The main panel in the house is 200 amp service about 130 feet away. What size / type copper wire should I use and what size underground conduit should I use? How deep should the conduit be buried. Thanks PTC
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 3, 2007, 12:02 PM
    #2 THHN/THWN or XHHW Copper, or #1 XHHW aluminum will produce just under 2 % voltage drop for a fully loaded to 80% for a 100 amp feeder.

    In either case I would use no smaller than 2" PVC, due to the length, and allow for expansion.

    If this is residential, 18 deep, otherwise 24 " deep.

    Be sure to have a #6 equipment grounding conductor, and keep the neutral insulated at the subpanel.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running two 100 amp main panels from a 200 amp service [ 27 Answers ]

Greetings! I live in a rural country area. The electric company will be installing a pole, meter, and 200amp service with disconnect at pole. (It will require 50 foot run of service cable from pole to main load center in mobile). Currently the double wide has a General Electric 100amp Main...

100 Amp Service [ 3 Answers ]

I am looking at purchasing a home that has the wire from the mast running into a 100 cut-off switch, then into a 60 amp panel. Would it be possible to change out the 60 amp panel to a 100 amp panel?

100 amp service vs. 200 amp service [ 4 Answers ]

:) I am looking at a small (totally remodeled home) with 100 amp service. I always thought it was better to have 200 amp. I will live there alone. Does this mean I can't run the dryer and microwave at the same time?

Using 100 amp panel on 200 amp service [ 5 Answers ]

I am building new camp at a site that already has 200 amp service. My power requirements are small and 100 amp will be more than sufficient. Is there any reason I cannot hookup a 100 amp panel to the 200 amp meter socket? Not sure is code allows this. I want to use a small 100 amp panel vs the...

100 amp service vs. 200 amp service [ 5 Answers ]

The house I just bought was built in 1952. It's a 3 bedroom, 1 bathroom with the standard screw in fuses (total amps unknown). Presently I'm doing a remodel. Adding a third bedroom & extra bathroom, washer & dryer, dishwasher, newer & larger refrigerator, bigger microwwave, probably 3 window air...