    Wiring a sub panel
    I am installing a small 120v sub panel in my basement. The builder pre-wired from the main service panel a #10 four wire (red, white, black & ground) to my basement. I purchased a small Square D panel and two 30 amp breakers. The box I purchased has no ground bar, only a neutral bar. I know that the white wire goes to the neutral bar. Where do the other wires go?:confused:

    The service panel I purchased is a Square D Homeline 70 A with two spaces HOM24L70SPC. I bought a ground bar kit to attach.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Oct 1, 2007, 06:25 PM
    Black goes to a main lug. Red goes to the other main lug. Neutral needs to be isolated from ground. You need a ground bar kit.

    What's the make and model of the "sub-panel"?

    There is a chance you have a main panel. Does the panel have a main breaker? It shouldn't.

    #10 is only rated for 30 A if it's a single cable. It should be fed from the main panel from a 30 A breaker. 40 AMP if single conductors in conduit. See reference later. Typo on my part.

    Edit: Changed the current ratings. Thanks labman.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #3

    Oct 1, 2007, 07:35 PM
    If the 4 wires are bundled together in an orange jacket, it is NM-B and only rated for 30 amps. We have a great electrician here posting under tkrusell. I think you would be better off ignoring the first answer and waiting for one you can trust.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Oct 1, 2007, 08:45 PM
    labman:

    My reference: Okonite Ampacity Tables: NFPA 70, National Electrical Code, 600 Volt Ampacity Tables

    Where is yours?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #5

    Oct 1, 2007, 08:59 PM
    If the builder ran conduit and pulled THNN, then 40 amps may be correct. Unless the OP lives in Chicago, likely it is the 30 amp NM-B. I have seen a lot of terrible answers here where somebody knowing little of the subject did a search and found a web page that didn't apply.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Oct 2, 2007, 04:34 AM
    Kiss, note the disclaimer Okonite has for this wire ampacity chart:

    *Ampacities are maximum allowed by the National Electrical Code.

    The provided chart is a bit misleading, as it does not reflect the entire wire ampacity Table 310.16 as shown in the NEC.

    Table 310.16 has a disclaimer directing to Section 240.4(D), that reduces the maximum of #14 to 15 amps, #12 to 20 amps, and #10 to 30 amps, for all but for specific installations and insulations.

    Then one must consider Section 334.80, which only allows any NM-B cable, AKA Romex, to the 60 Deg C column of NEC table 310.16.

    Your statement regarding #10 wire: "40 AMP if single conductors in conduit." is incorrect for this particular installation.

    40 Amp would only be allowed on a #10 wire if the installation falls under those listed 240.4(E) or (G), AND if the equipment has terminals rated for 90 Deg C.

    For normal, routine, general purpose wiring, #10 can only be rated 30 amps, no matter if Romex cable or pulled THHN wires is used.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Sub Panel Wiring [ 20 Answers ]

I'm running power to a new shop which is about 125 feet from the house. I would like to have 75 amp service at the shop. The service at my house is 200 amps and there is space in the panel for an additional breaker. I also have a separate 200 amp switch located next to the main panel that is used...

Wiring to sub-panel. [ 1 Answers ]

Will this work properly if when wiring a sub-panel for 240v can one of the 3 aluminum 4 gauge wires in the pvc underground pipe be used as the neutral wire if that wire is bare? I intend to attach the ground bus at the sub-panel to a ground rod using 6 gauge bare copper wire.

Main to Sub Panel Wiring [ 3 Answers ]

I received an answer prior to wiring this up, but am a bit confused. I think I was told to keep the ground separate at the sub panel but am not sure. If so, I only need to pull 3 wires (2 hot legs and 1 neutral). I have attached my PDF for your review. Thanks, ...

Sub panel wiring [ 1 Answers ]

I have a 50 amp GFCI breaker in my subpanel box to be used by a hot tub. I noticed that the breaker has a post for the neutral wire load. Is it necessary to use this post or can my load neutral wire be connected to the neutral bus (same as breaker pigtail and supply neutral)?

Sub panel 40 amp wiring [ 1 Answers ]

I have a 70 amp sub panel. I'm trying to figure out how to wire in a 40amp breaker in the sub from the panel in my house. I have two hot wires coming in to separate lugs, one neutral, but the breaker itself has one trip/reset lever yet has two screws on the bottom of the breaker;one on each side....


View more questions Search