    200 amp service ground
    I am replacing an old 200 amp meter base with a 200 amp meter base with a built in disconnect breaker. From here I will feed the 200 amp panel inside.

    My question is about the ground. I have PEX plumbing, but the supply to the house is galvanized. I understand I need to bond the water supply to the grounding system, I have 2 grounding rods 6' apart that will be the main ground. I need to understand where the grounds will connect. If I understand correctly, since the new meter base will have a disconnect, the ground needs to be bonded to the neutral at the disconnect. So does this mean that my 2 ground rods will connect to the meter disconnect and not the inside panel?

    If that is correct, then I have 4/0 from the meter to the panel for the two hots, and the neutral is a 2/0. Is this the correct size for the neutral? I read in my code book that the neutral should only be bonded to ground at the first disconnect, so I won't bond it on the inside panel, but my question then is what is connected to the ground bar on the inside panel? Do I need to run another #6 wire from the panel ground bar to the ground rods? And where should the water main be bonded?

    Thanks a bunch!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 29, 2007, 05:02 AM
    With the main at the meter, the neutral will be bonded to the metal can , and connect both incoming and outgoing neutrals, grounding electrode conductor from ground rods, and an outgoing equipment grounding conductor to the panel.

    The feed from the meter/disconnect to the panel must be four wire, 2 hots,1 neutral, and 1 equipment ground, which should be a min of #6 copper or #4 aluminum, insulated. This #6 will connect to the equipment ground bar in the panel, along with all branch circuit equipment grounding wires.

    Bonding the water can be done from the panel's equipment grounding bar, to any point of the metal water piping that is accessible.

    The neutral can be reduced down to #2/0 if the service calculations have been done, which then shows the amount of neutral current. The neutral can be reduced down to 70% of the mains.


    Hope this helps.
    hardwiredman's Avatar
    hardwiredman Posts: 11, Reputation: 1
    New Member
     
    #3

    Sep 29, 2007, 12:25 PM


    Is this correct?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Sep 30, 2007, 03:14 AM
    Exactly.
    hardwiredman's Avatar
    hardwiredman Posts: 11, Reputation: 1
    New Member
     
    #5

    Sep 30, 2007, 10:36 AM
    Quote Originally Posted by tkrussell
    Exactly.
    Thank you very much, you've been very helpful.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Sep 30, 2007, 11:40 AM
    In addition to above, Noticed bonding screw is out, and should stay out.
    We commonly run a #6 to the Cold IN on the water heater. Easy, protected, and accessible.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running 100 amp service panal 200 ft away from main 200 amp service [ 4 Answers ]

I am looking to find out how big the wire needs to be to carry the load. This will be a 100 amp service coming from a 200 amp main . It will need to travel 200 to 250 ft underground to a barn. If some one could help me that would be great thaxs)))

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...

100 amp service vs. 200 amp service [ 4 Answers ]

:) I am looking at a small (totally remodeled home) with 100 amp service. I always thought it was better to have 200 amp. I will live there alone. Does this mean I can't run the dryer and microwave at the same time?

200 amp service with a 200 amp outdoor breaker [ 1 Answers ]

I need to know how to wire a 200 amp outdoor breaker enclosure.I have 4/0 scu cable for my service head to the meter,and 4/0 scu from meter to breaker enclosure.Then from the breaker enclosure I have 4/0 ser cable to my panel.What is the proper wiring method in the enclosure,please help.


View more questions Search