Ask Experts Questions for FREE Help !
Ask
    redsled's Avatar
    redsled Posts: 1, Reputation: 1
    New Member
     
    #1

    Sep 20, 2007, 10:18 AM
    Circuit breaker
    How can I check a circuit breaker, several switches/plugs do not work, but none of the breakers is tripped.
    icecream's Avatar
    icecream Posts: 160, Reputation: 6
    Junior Member
     
    #2

    Sep 20, 2007, 10:34 AM
    Why would you want to check them if it isn't triipped? If your just curious DON'T! If you ar.

    All panels have a main disconnect. Make sure that is off and go from there.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Sep 20, 2007, 12:55 PM
    This is a frivolous post by Ice Cream with a useless, condescending answer.

    An outlet with no power and no tripped breakers will most likely be a loose connection somewhere in the circuit, anywhere from the breaker to any wire in any outlet or junction box.


    You will need a voltage tester. If you know which circuit breaker feeds the outlets with no power, try opening the last working outlet on the circuit looking for a loose wire connection on the back of the outlet.

    If the wire connections are push in the back type, these are popular causing loose connections. Change any push in style connection to wrapped around the screw connection.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #4

    Sep 20, 2007, 01:44 PM
    I agree with Kevin, what a goofy answer from Icecream. Are all of your nonworking outlets on the same circuit? Do any outlets on this circuit work or is the entire circuit out?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Sep 21, 2007, 02:14 AM
    I would not rule out a tripped breaker just yet. Sometimes the breaker handles don't have enough throw on them to be seen as open. If you know the breaker, turn the breaker all the way off and then back on and let's see what happens.

    If you are seeing a complete dead circuit I would bet on there being an open connection within the circuit, get out a meter and start checking. I would look for voltage first.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Sep 21, 2007, 06:14 AM
    Sometime breakers will trip, but will not "throw". Sometimes you can run your finger down each row of breakers lightly, Not enough to turn off, but enough to expose tripped breaker. Someone may have wired onto GFI circuit, Test for power at your GFI's.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Circuit breaker [ 3 Answers ]

Circuit breaker will not reset

Circuit breaker [ 1 Answers ]

How does one change circuit breaker? It doesn't click into place, it's just very mushy & loose.

Circuit breaker [ 1 Answers ]

I have a 15 amp circuit breaker tied to some outlets and when my sprinkler system was installed they tied into this line. Sometime when using more than 1 thing and running the sprinkler it trips. Can I increase this to a higher amperage safely?

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!


View more questions Search