Ask Experts Questions for FREE Help !
Ask
    Sager's Avatar
    Sager Posts: 31, Reputation: 4
    Junior Member
     
    #1

    Sep 19, 2007, 12:52 PM
    Circuit Breaker Difference and Wiring Requirement
    Is a 20 amp 2 pole Tandem, the same as a 20 amp 2 pole ?
    I do not know which breaker to use - i.e. one about 1 inch wide or
    The one that is about twice that size. Also, what gauge wire and
    Breaker size do I need for the following:

    I bought an Wall Oven and Drop In Cooktop
    The data plate on the Wall Oven shows:
    208Y/120V Kw 2.7
    120/240V Kw 3.6

    The data plate on the Drop In Cooktop shows:
    /208V 5.00 Kw
    /240V 6.70 Kw
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 19, 2007, 04:16 PM
    No, a tandem is two separate switches in one housing designed to plug onto only one hot bus of a panel. Note that is will only be rated 120 volts. A true 2 pole breaker will be rated 120/240 and have a common trip internally between poles, and designed to plug onto both hot bus of a panel.

    Watch out, some manufacturers make "half size" two pole breakers, they look like tandems. Read the data on the box or label on the breaker. These are fine for space saving in a panel when needed. Confusion is they look like tandem breaker which may get used instead of a true 240 volt 2 pole breaker.

    A standard 2 pole breaker will be full size, usually 2 inch wide, and a handle across both poles.



    Assuming you have a single family home with typical 120/240 volt service:

    While both units total 10300 watts, you are allowed to connect both of these to one feeder to be considered as one standard range, and rate the circuit at a demand rate of 8000 watts, and run the minimum size feeder of 40 amp.

    This will require a minimum of #8-3 plus ground NM-B Romex cable.

    At the oven or cooktop, stop the 8-3 in a junction box and connect the two whips, one from each appliance, use all the proper cable connectors, and splice in a 4-11/16 inch square junction box, using large blue wirenuts, and cover the box with the proper junction box cover.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

How do I balance my breaker box and How much of a difference can it make? [ 4 Answers ]

Hi, I have found this site very helpful. Thanks. My question was that someone brought up that I should balance my breaker box to save on the electric bill. I understand the concept of it but was looking for more information about it. The house has 150 amp service just so everyne knows. ...

Circuit breaker [ 3 Answers ]

A circuit breaker connected to the kitchen tripped twice. I had an electrician in but the problem persists - in fact, the very day the electrician came. It does not seem to be caused by any one particular appliance. The first time I was using the waste disposal and the next two times nothing was...

Circuit breaker [ 1 Answers ]

I have a 15 amp circuit breaker tied to some outlets and when my sprinkler system was installed they tied into this line. Sometime when using more than 1 thing and running the sprinkler it trips. Can I increase this to a higher amperage safely?

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!