    Condenser fan stops running after awhile
    I have central air and after the air has been on awhile, the condenser fan stops running.
    The outside unit is still on because it makes a bit of a racket, just no longer the fan. I don't know what is causing the noise, maybe vibrating, because as soon as I'm aware the fan isn't running, I shut it off. If I turn it back on 10 minutes later, it works fine again. It's been doing this off and on for about a week.

    Any ideas?

    Thanks,

    Jim
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Sep 5, 2007, 03:10 PM
    Sounds like the outside fan is going out on the internal overload due to a high curent draw or lack of air flow. You might try giving the outside coil a good cleaning to see if that improves the air movement.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #3

    Sep 5, 2007, 06:08 PM
    You may have a defective capacitor for the fan motor, try replacing this if it still gives you a problem you probably have a bad motor.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #4

    Sep 5, 2007, 06:39 PM
    Can you check to see if you still have voltage going to the condenser fan motor when it stops running? If you do have voltage it means that it is something wrong with the motor, if you don't have voltage it means that you have a problem with the contactor.

    If you have voltage and the motor seems to be unusually hot I would recommend a good oiling if you have oil holes, so many of the newer motors do not have places to oil.
    inthecountry's Avatar
    inthecountry Posts: 5, Reputation: 1
    New Member
     
    #5

    Sep 6, 2007, 06:12 AM
    Quote Originally Posted by hvac1000
    Sounds like the outside fan is going out on the internal overload due to a high curent draw or lack of air flow. You might try giving the outside coil a good cleaning to see if that improves the air movement.
    I usually rely on how the outside of the coils look to decide if I should clean them or not.
    Perhaps this isn't the best way to go. I will make sure those coils are good and clean.

    Thanks for your response,

    Jim
    inthecountry's Avatar
    inthecountry Posts: 5, Reputation: 1
    New Member
     
    #6

    Sep 6, 2007, 06:19 AM
    Quote Originally Posted by letmetellu
    Can you check to see if you still have voltage going to the condenser fan motor when it stops running? If you do have voltage it means that it is something wrong with the motor, if you don't have voltage it means that you have a problem with the contactor.

    If you have voltage and the motor seems to be unusually hot I would recommend a good oiling if you have oil holes, so many of the newer motors do not have places to oil.
    I will check for voltage the next time this happens. I will also research to find out if my motor can be oiled or not. Is there an easy way to see if it can be oiled?
    inthecountry's Avatar
    inthecountry Posts: 5, Reputation: 1
    New Member
     
    #7

    Sep 6, 2007, 06:23 AM
    Quote Originally Posted by acetc
    You may have a defective capacitor for the fan motor, try replacing this if it still gives you a problem you probably have a bad motor.
    5 years ago, the capacitor was changed. Since it was only two years old then, testing the capacitor sure seems like a wise idea. I will take your advice.

    Thanks,

    Jim
    inthecountry's Avatar
    inthecountry Posts: 5, Reputation: 1
    New Member
     
    #8

    Sep 6, 2007, 11:55 AM
    Is there a brand of oil at a home center that I can use to oil the motor?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Sep 6, 2007, 12:48 PM
    3 IN 1 motor oil.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #10

    Sep 6, 2007, 06:30 PM
    To see if this motor can be oiled or not you need to look for two oil holes on the side of the motor, one at the top and one at the bottom. You can tell them because they will have a little plug in each hole. Now this does not mean they are directly on the end of the motor. You may have two plugs also on each end of the motor but these are drain holes and the only one of them that you remove is the one facing down after the motor is installed. Remember the oil holes are on the side of the motor. If you motor is black in the middle section and has a bright section on either end these holes will be in the bright section and they will be in line with each other.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

AC condenser fan not running nor is cool air [ 9 Answers ]

My condenser fan stopped running and there is no cool air coming from the vents. I'm wondering now though, will the cool air stop flowing just because the fan is not running, or does this mean that the compressor has gone bad? The compressor still turns on fine (it seems a bit nosier now though)...

1989 honda civic stalls out after running for awhile [ 2 Answers ]

I have a 1989 honda civic lx that has been a great car.Lately it wants to shut down after running for awhile. It starts fine in the morning or after sitting around.And when its running down the road its fine.It usually takes about 15 to 20 minutes for it to fail.It will not start up right away but...

Condenser fan stopped running [ 2 Answers ]

I have a miller condenser unit, and it stopped running. I hear everything else trying to run, the coils are getting super hot after 2-3 minutes, and the fan will not start running. What could be wrong?

Condenser Fan Overheats and stops running [ 7 Answers ]

Hello, My condenser unis is outside and the Fan kick starts fine when the unit turns on... but then after few minutes the condenser Fan (outside) stops... AC unit continues to run thus only resulting in pumping the hot air... It is happening over and over again... I am in Plano, Texas......

A/C stops running some times [ 3 Answers ]

My unit runs fine for a while and then suddenly stops. When it runs, I can measure 25VAC at the thermostat. When it stops, I have no 25VAC so I can not even run the fan in manual when it stops. After sitting for several hours, the system restarts and runs fine. I have checked the main...


View more questions Search