    15 amp switch on 20 amp circuit
    I am wiring a room with a 20 amp circuit. All of the receptacles are rated at 20 amps and I am running it all with 12 gauge wire. My question is when it comes to the switch for the ceiling fan/light, does the switch need to be rated 20 amp or can I use a 15 amp switch as the fixture probably doesn't even use more than 4 or 5 amps max and will never change. The back of the 15 amp switch says it accepts 14 or 12 gauge wire. Thanks!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 28, 2007, 11:17 AM
    No, a 20 amp circuit requires a minimum of 20 amp rated devices.
    rajeffer's Avatar
    rajeffer Posts: 4, Reputation: 1
    New Member
     
    #3

    Aug 28, 2007, 11:20 AM
    Ok, but from some of your other posts, you have 15 amp receptacles on 20 amp circuits (as long as the whole circuit is wired with #12 wire), so why is a 15 amp switch different? Perhaps because a receptacle/switch may say 15A on it, but it's actually rated for 20 amp?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Aug 28, 2007, 11:32 AM
    A 15 amp receptacle limits only a 15 amp plug to be inserted, thus limiting the load to 15 amps or less. A switch cannot do that. Anyone can come along and install larger lamps, add more fixtures, etc. and the switch can be overloaded.
    rajeffer's Avatar
    rajeffer Posts: 4, Reputation: 1
    New Member
     
    #5

    Aug 28, 2007, 11:46 AM
    You threw me off a bit when you said "a 20 amp circuit requires a minimum of 20 amp rated devices", cause I was reading all over the place that you could put a 15 amp device on a 20 amp circuit.

    Yep makes sense, so I think I will take out the 20 amp receptacles and replace those with 15 amp receptacles and then make my switch a 20 amp switch - and I should be good to go. Thanks for the advice!
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Aug 28, 2007, 11:51 AM
    Yes, my wording was a bit confusing, I should have used the word "switch" and not " devices, since 15 amp receptacle can be on a 20 amp circuit.

    Sorry for the confusion.

    Leave the 20 amp receptacles and only buy the one 20 amp switch. This will save you some work and money.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

20 AMP Circuit with 15 AMP Receptical, is this OK, and in code? [ 5 Answers ]

This is sort of similar to the other thread, but my problem is the house I bought is wired with 12, all the breakers are 20AMP except for the 30AMP for the AC and Dryer. When me and my dad were changing the power recepticals, which were 15 amp, someone told us that we should have 20 recepticals, or...

15 amp outlet on 20 amp circuit [ 5 Answers ]

Can I use a 15 amp outlet on a 20 amp circuit. Wire with 12 gauge wire.

Changing a circuit breaker from 25 amp to 20 amp [ 2 Answers ]

My air conditioner is on a 25 amp breaker and should be on a 20 amp max (per manufacturing). All I need to do is take out the old one and install the new one- right. Do I need to worry about the size of wire when installing a lower breaker or just when increasing it?

40 amp range in 30 amp circuit [ 1 Answers ]

I have a 30 in drop in range that is hard wired. The circuit breaker is 30 amps, house built in 1987. The new range is a slide in and requires 40 amps. I was told I would also need a junction box installed and circuit upgrades. How many hours are expected for an experienced electrician to do...

20 amp device on 15 amp circuit [ 1 Answers ]

I'm new to wiring, don't profess to be an expert, learned how to do it through reading books, and admit I need some help. I'm currently finishing my basement and just finished up adding two 15-amp circuits for lights and receptacles. Part of my longer range goal is to add a sauna. The kits...


View more questions Search