    Adding lights to circuit
    I have a 15 amp fuse that runs 8 - 75w bulbs. I would like to add 6 can lights with 65w bulbs. Can I do that on the existing circuit? Also will these can lights work with the existing #14 wire that is installed or do I need to use #12wire?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Aug 25, 2007, 07:47 AM
    120 volts X 15 Amps = 1800 Watts, Derated 80%(1800 X .8=1440 Watts Maximum).
    (8 X 75 = 600 Watts), + (6 X 65 = 390 Watts), = 990 watts.
    1440 Watts -990 Watts= 450 watts to spare.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Aug 25, 2007, 12:45 PM
    If this is a basement, or any dark area, consider pulling a new circuit. If one circuit fails, the other will continue to work.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Aug 25, 2007, 04:27 PM
    I agree with redundancy, one circuit handling many lights can leave you in the dark, should breaker trip.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #5

    Aug 26, 2007, 01:05 PM
    Derated 80%(1800 X .8=1440 Watts Maximum).
    anyone want's to get more into the 80% rule? I guess I can't say the OP should have asked why, or why not, because they haven't checked back yet.
    kelbo's Avatar
    kelbo Posts: 3, Reputation: 1
    New Member
     
    #6

    Aug 26, 2007, 03:45 PM
    Quote Originally Posted by kelbo
    I have a 15 amp fuse that runs 8 - 75w bulbs. I would like to add 6 can lights with 65w bulbs. can I do that on the existing circuit? Also will these can lights work with the existing #14 wire that is installed or do I need to use #12wire?
    What is the 80% about...

    Yes it is for a basement and I potentially may be using 3 6" can lights and up to 8 4"can lights since the spacing of the ceiling tiles are not conducive for the 6-6" can lights. So will this be a problem or am I just safer in installing a new fuse and creating a new circuit... also can I tap to this circuit in the future for a small bathroom?

    Thanks for you help
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #7

    Aug 27, 2007, 05:17 AM
    The code was re written a bit a few years ago. Many electricians will remember and default to any circuit can only be loaded to 80 % of the circuit rating.

    Now, technically, the code is written that if the load is continuous the laod can be 100 % of the circuit rating , and any load that will run 3 hours or more must be derated 80%, or 125% of the actual load.

    This gets confusing, esp for us older electricians that have been doing it one way for many years.

    This is not usually a problem with residential, as very few loads actually will run more than 3 hours. In commercail or industrial just about everything will run more than 3 hours, so we derate everything 80 %.

    Pulling a new circuit is recommedned, but not required.

    Bathroom receptacles need to be on a dedicated 20 amp circuit. Lights and fan can be on another circuit. Or one circuit can handle outlet, lights, and fan for that one bathroom.

    Clear as mud?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Adding a circuit [ 3 Answers ]

I'm finishing a basement and think it's best to start fresh with a new circuit for a room we're building. There is a spare circuit breaker already in the panel (30 amps), so I suppose I could just run the 12 gauge wire from it (no need to change to 20 amp breaker?). Also, how many more 20 amp...

Adding extra lights [ 4 Answers ]

I have wired up 5 extra down light in a circuit. When I turn them on, they dim and if I remove one they all go out. What amI doing wrong?

Adding a new circuit? [ 13 Answers ]

Hello, I am in the process of adding a basement bathroom and I have a couple of questions about the wiring. I plan to have a wall mounted light over the vanity, fed from a gfci outlet also at the vanity. I am going to have a ceiling fan/light as well as a shower light. I do have room in the panel...

Adding a heater to an existing circuit. [ 3 Answers ]

I want to place a 240V electric base board heater in a room. In the adjacent room I have a conveniently placed electric wall oven by itself on a 50 Amp circuit with 8 gauge wire. The oven is only rated at 30 Amps and the heater at 4.5 amps. So, I want to run wire from the oven to where the...

Lights out but circuit is hot [ 1 Answers ]

Here is the situation, 2 wall outlets, 1 fluorescent, and 9 celing cans all on the same circuit. 6 of the cans are controlled by a pair of 3 way switches, the other three on single pole switches. Nothing works. The circuit breaker doesn't trip and I have reset it several times. What happens is...


View more questions Search