Adding lights to circuit
I have a 15 amp fuse that runs 8 - 75w bulbs. I would like to add 6 can lights with 65w bulbs. Can I do that on the existing circuit? Also will these can lights work with the existing #14 wire that is installed or do I need to use #12wire?
|
|
 |
Uber Member
|
|
Aug 25, 2007, 07:47 AM
|
|
120 volts X 15 Amps = 1800 Watts, Derated 80%(1800 X .8=1440 Watts Maximum).
(8 X 75 = 600 Watts), + (6 X 65 = 390 Watts), = 990 watts.
1440 Watts -990 Watts= 450 watts to spare.
|
|
 |
Uber Member
|
|
Aug 25, 2007, 12:45 PM
|
|
If this is a basement, or any dark area, consider pulling a new circuit. If one circuit fails, the other will continue to work.
|
|
 |
Uber Member
|
|
Aug 25, 2007, 04:27 PM
|
|
I agree with redundancy, one circuit handling many lights can leave you in the dark, should breaker trip.
|
|
 |
Senior Member
|
|
Aug 26, 2007, 01:05 PM
|
|
Derated 80%(1800 X .8=1440 Watts Maximum).
anyone want's to get more into the 80% rule? I guess I can't say the OP should have asked why, or why not, because they haven't checked back yet.
|
|
 |
New Member
|
|
Aug 26, 2007, 03:45 PM
|
|
 Originally Posted by kelbo
I have a 15 amp fuse that runs 8 - 75w bulbs. I would like to add 6 can lights with 65w bulbs. can I do that on the existing circuit? Also will these can lights work with the existing #14 wire that is installed or do I need to use #12wire?
What is the 80% about...
Yes it is for a basement and I potentially may be using 3 6" can lights and up to 8 4"can lights since the spacing of the ceiling tiles are not conducive for the 6-6" can lights. So will this be a problem or am I just safer in installing a new fuse and creating a new circuit... also can I tap to this circuit in the future for a small bathroom?
Thanks for you help
|
|
 |
Uber Member
|
|
Aug 27, 2007, 05:17 AM
|
|
The code was re written a bit a few years ago. Many electricians will remember and default to any circuit can only be loaded to 80 % of the circuit rating.
Now, technically, the code is written that if the load is continuous the laod can be 100 % of the circuit rating , and any load that will run 3 hours or more must be derated 80%, or 125% of the actual load.
This gets confusing, esp for us older electricians that have been doing it one way for many years.
This is not usually a problem with residential, as very few loads actually will run more than 3 hours. In commercail or industrial just about everything will run more than 3 hours, so we derate everything 80 %.
Pulling a new circuit is recommedned, but not required.
Bathroom receptacles need to be on a dedicated 20 amp circuit. Lights and fan can be on another circuit. Or one circuit can handle outlet, lights, and fan for that one bathroom.
Clear as mud?
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Adding a circuit
[ 3 Answers ]
I'm finishing a basement and think it's best to start fresh with a new circuit for a room we're building. There is a spare circuit breaker already in the panel (30 amps), so I suppose I could just run the 12 gauge wire from it (no need to change to 20 amp breaker?). Also, how many more 20 amp...
Adding extra lights
[ 4 Answers ]
I have wired up 5 extra down light in a circuit. When I turn them on, they dim and if I remove one they all go out. What amI doing wrong?
Adding a new circuit?
[ 13 Answers ]
Hello, I am in the process of adding a basement bathroom and I have a couple of questions about the wiring. I plan to have a wall mounted light over the vanity, fed from a gfci outlet also at the vanity. I am going to have a ceiling fan/light as well as a shower light. I do have room in the panel...
Adding a heater to an existing circuit.
[ 3 Answers ]
I want to place a 240V electric base board heater in a room. In the adjacent room I have a conveniently placed electric wall oven by itself on a 50 Amp circuit with 8 gauge wire. The oven is only rated at 30 Amps and the heater at 4.5 amps. So, I want to run wire from the oven to where the...
Lights out but circuit is hot
[ 1 Answers ]
Here is the situation, 2 wall outlets, 1 fluorescent, and 9 celing cans all on the same circuit. 6 of the cans are controlled by a pair of 3 way switches, the other three on single pole switches. Nothing works. The circuit breaker doesn't trip and I have reset it several times. What happens is...
View more questions
Search
|