    Adding subpanel for basement workshop
    Hi -
    I have 200 amp service to my home and would like to add a workshop in the basement with a separate subpanel. The run from the main to the sub will be short (< 10 ft) so voltage drop should not be a problem.

    I have been advised to take 240v. via a dual pole 30 amp CB from the main to the sub and then two or three circuits off the sub to various junction boxes for the tools (table saw, chop saw, power vac. Etc ). Lights are on a separate circuit from the main panel.

    First off does this sound like a good plan? What wire size would you use for the run?

    Thanks in advance for your help

    SSB
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Aug 25, 2007, 12:31 PM
    Plan sounds modest and reasonable. Use 4 wire #10 cable with a green or bare ground.

    Be sure to keep the neutral insulated from the metal case of the panel, and connect all grounds to a ground bar mounted directly to the metal case.
    ssb's Avatar
    ssb Posts: 3, Reputation: 1
    New Member
     
    #3

    Aug 25, 2007, 12:47 PM
    Quote Originally Posted by tkrussell
    Plan sounds modest and reasonable. Use 4 wire #10 cable with a green or bare ground.

    Be sure to keep the neutral insulated from the metal case of the panel, and connect all grounds to a ground bar mounted directly to the metal case.


    Modest? Do you think more power is in order (i.e. 40-60 amp)?
    Also, does the subpanel need to be grounded separately (i.e. to it's own rod) or can it be grounded to the ground in the main?

    Thanks again for your expertise
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Aug 25, 2007, 12:50 PM
    Quote Originally Posted by ssb
    Hi -
    I have 200 amp service to my home and would like to add a workshop in the basement with a separate subpanel. The run from the main to the sub will be short (< 10 ft) so voltage drop should not be a problem.

    I have been advised to take 240v. via a dual pole 30 amp CB from the main to the sub and then two or three circuits off the sub to various junction boxes for the tools (table saw, chop saw, power vac. etc ). Lights are on a separate circuit from the main panel.

    First off does this sound like a good plan? What wire size would you use for the run?

    Thanks in advance for your help

    SSB
    I'd probably put a 60 amp breaker in the main panel. You would need 6/3 or 8/3 copper with ground. Neutral and ground are not connected together in the sub-panel. The sub-panel does not need a main breaker

    Here is a thread as to how not to do it: https://www.askmehelpdesk.com/electr...re-122146.html

    I posted this link in that thread for a good overview:

    Adding New Electrical Circuits - Installing A Sub-Panel - An Overview

    Something to think about while wiring the shop is what might be necessary for a central dust collecting system. If you plan for separate circuits, you can easily place current sensors in the panel or a separate panel that would turn on the vacuum when the power tool was turned on. SSAC, ABB SSAC Timers & Controls Fast Facts (800) 377-SSAC(7722) makes some nice sensors. An example: http://www.ssac.com/catalog/ECS01A01.pdf

    What I would envision is a separate NEMA 1 enclosure where the wires would initially enter and then a large conduit like 2" or so connecting to the Breaker panel. They would enter into the NEMA 1, go through the current sensor and on to the breaker. Nice, clean, simple and add sensors as you need to.

    It's something to think about. It's much easier to do it now than add later.
    ssb's Avatar
    ssb Posts: 3, Reputation: 1
    New Member
     
    #5

    Aug 25, 2007, 01:04 PM
    Quote Originally Posted by KeepItSimpleStupid
    I'd probably put a 60 amp breaker in the main panel. You would need 6/3 or 8/3 copper with ground. Neutral and ground are not connected together in the sub-panel. The sub-panel does not need a main breaker

    Here is a thread as to how not to do it: https://www.askmehelpdesk.com/electr...re-122146.html

    I posted this link in that thread for a good overview:

    Adding New Electrical Circuits - Installing A Sub-Panel - An Overview

    Something to think about while wiring the shop is what might be necessary for a central dust collecting system. If you plan for separate circuits, you can easily place current sensors in the panel or a separate panel that would turn on the vacuum when the power tool was turned on. SSAC, ABB SSAC Timers & Controls Fast Facts (800) 377-SSAC(7722) makes some nice sensors. An example: http://www.ssac.com/catalog/ECS01A01.pdf

    What I would envision is a separate NEMA 1 enclosure where the wires would initially enter and then a large conduit like 2" or so connecting to the Breaker panel. They would enter into the NEMA 1, go through the current sensor and on to the breaker. Nice, clean, simple and add sensors as you need to.

    It's something to think about. It's much easier to do it now than add later.

    Thanks for the ideas on the current sensors and the overview link...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Adding a Subpanel to a shed [ 7 Answers ]

I planning on adding a subpanel to my shed. I think I have done my homework and here is what I was planning. I was going to add double pole (40AMP 240 volt breaker) to my main panel. It is about an 80 foot run between my main panel and the subpanel I am adding. I already have schedule 80 PVC...

Adding GFCI Breaker to Existing Subpanel [ 4 Answers ]

I want to add a GFCI breaker to an existing sub panel (used to power a hot tub) so I can have a protected outlet on my patio. However, I'm confused as to how to wire in to the existing wiring. The existing sub panel has a double pole 50A breaker with 2 hot wires (red and black) and a neutral...

Basement subpanel. [ 1 Answers ]

Thanks in advance for all help involved in my endeavors... First off let me start by saying this is an old home built in 1959 and has all fusible circuits.. The home was somewhat upgraded as far as I can tell in the 70`s with an exterior meter panel with breaker space for extra circuits,but by and...

Adding subpanel [ 6 Answers ]

I have a 200A main panel in my garage and want to install a subpanel in my basement to feed 4 circuits (15 & 20 A). The best route I can find for the feeder wire is through the garage in conduit, then entering the basement through the concrete foundation. I have a couple of questions. 1. If I...

Adding subpanel [ 1 Answers ]

I'm converting my garage to a woodshop, so I need 220 service for the table saw and band saw, and potentially later the dust collector and compressor. Also I want to run a new circuit for lights, plus two 110 outlet circuits. That's a possible four 220 and three new 110 circuits. I've got a...


View more questions Search