    Hi All,

    I need to install a small tankless water heater (made for under the lavatory sink) for the sink in my bathroom. The specs on the water heater are: 120 Volts, 2.4kW, 20 Amps, wire size: 10AWG. My question is this... The existing bathroom outlet that I want to splice into to add this water heater on has a 15Amp breaker. Can I add a 20 amp receptacle using the same house wiring that is in place (the home was built in Palm Beach county, Florida in 1991) and I think it is either 12 or 14 gauge. To make this a 20A circuit, do I simply need to change the 15A breaker to a 20A breaker? The only device that will need the 20A is this new water heater, do I need to change ALL the receptacles on this breaker to 20amp receptacles? All advice will be helpful.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 17, 2007, 04:51 PM
    Sorry but no short cuts here, you will need a new 30 amp circuit, complete with a 30 amp single pole circuit breaker , #10-2 cable, and a 30 amp 125 volt straight blade NEMA 5-30R outlet, and large outlet cover.

    The branch circuit rating needs to be 125% of the running load, and that is 25 amps and exceeds the rating of #12 wire.

    You can make up a #10-3 cord with the NEMA 5-30P plug, this will serve as the service disconnect.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #3

    Jul 17, 2007, 05:00 PM
    This heater pulls 20 amps, number 12 wire is good to 20 amps number 14 wire is only good for 15 amps, they recommend number 10 wire and since it is right on the top edge of a 20 amp breaker , I would suggest a 30 amp breaker because it would be less likely to cause breaker tripping problems. The 10 gage wire would be properly sized for a 30 amp breaker, this heater should be on a breaker by itself.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Switching from 15AMP breaker to 20AMP [ 6 Answers ]

I am contemplating switching my 15AMP breaker into a 20AMP breaker because the lights flicker in my home office because my computer and printer eat up a lot of power. If I switch breakers, will this help my power problem? Or I am limited to the gauge of the wires in the wall? Thanks for the...

20amp vs. 15amp outlets [ 6 Answers ]

Is there anything inherently different between 15amp and 20amp outlets? Outlets labeled 20a are about 3-4 times more expensive than the ones labeled 15a. My buddy with a fair amount of experience advises me to buy 15a outlets and hook them up to my 12 gauge wire running back to 20amp breakers. ...

20amp circuit breaker, 15 amp receptacles [ 2 Answers ]

I have a 20amp circuit breaker with 15 amp receptacles and light switches on #12 wire with a load of 1700, is this allowable? If not, and I change to a 15 amp circuit breaker, is the 1440 watt safety load in the code or is it a non-code safety suggestion?

15amp or 20amp? [ 2 Answers ]

Does the 2005 NEC allow bedroom and living room outlets to be on a 15amp circuit? I am familiar with the 80% rule. Thanks in advance. Tom

Outside GFI circuit - 15amp outlet on 20amp circuit [ 1 Answers ]

I need a better understanding of what I should do when setting up my new outdoor circuit. I've got a circuit that runs about 150 feet, so I'm installing 10g wire to allow for the voltage drop. I read in the Home Depot Electrical 123 book that I can have at most a 15amp circuit with 10g wire on...


View more questions Search