    Units CONSTANTLY freezing up
    I have a 10,000 square foot building that has four new 5 ton Ruud units outside. All four units are icing up around the compressor. All units have been cleaned, freon checked, blower motor checked, grills checked, air filters replaced, thermostats replaced and copper lines coming out of compressor replaced with bigger lines. Nothing has worked. Three different repairmen have looked at these units and agree that its an air flow problem. These units freeze up during the day and night, but mostly at night. What could possibly be causing this? Any suggestions will be greatly appreciated. Thanks.

    Addition to question -When units are first turned on and not frozen it seems that air is not coming out of vents into building fast enough. Inside units were checked as well. Servicemen say that duct work looks okay.
    One did mention something like a tornado effect may be happening.
    XenoSapien's Avatar
    XenoSapien Posts: 627, Reputation: 42
    Senior Member
     
    #2

    Jul 15, 2007, 05:01 AM
    Have the A-Coils been checked?

    XenoSapien
    mkcav's Avatar
    mkcav Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 15, 2007, 07:13 AM
    Quote Originally Posted by XenoSapien
    Have the A-Coils been checked?

    XenoSapien
    I will check on that. Thanks for the reply. It is very humid where I live. Would that have anything to do with it?

    Melissa
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jul 15, 2007, 08:13 AM
    New 5 ton Ruud units outside

    New units should be under warranty by the installer. Have them do the work or your warranty might go out the window.

    Air recirculation. Sucking supply air right back into the return air. This will make them freeze up pronto.

    Improper location of thermostat.

    Dirty air filters.

    Someone played with the refrigerant charge and now the units freeze up.

    Many open large buildings we did over the years were helped quite a bit by using industrial ceiling fans to force more air circulation.
    acetc's Avatar
    acetc Posts: 1,004, Reputation: 79
    Ultra Member
     
    #5

    Jul 15, 2007, 10:00 AM
    You mention mostly at night, this could mean you may be operating the thermostats too low, they should never be set below 70 degrees unless they were designed for this as in a computer room. If your service person checks the temperature across the evaporator coil he will be able to determine if it has proper air flow (should be about 20 degrees differential) If it is higher , say around 24 that shows not enough air flow, duct sizing is one thing that needs to be checked to provide proper air flow. Are the fan coils on a timer to shut them off at night? Not shutting off condensing units? Also, you might want to check your programing on the thermostat to insure it is not dropping the cool setting at night instead of raising it. (assuming you have a programable)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Jul 15, 2007, 11:02 AM
    DEpending upon the outdoor temperature you might have to install low ambiant kits for the condenser fan motors.

    Try fan handler LOOK under products list on left.

    FanHandler.com

    The owner will only sell to a listed HVAC company. No do it yourselfers allowed. They work great been using them for years.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to convert units [ 15 Answers ]

Here is the question: Our sun is 93 million miles away... the speed of light travels at 186 thousand miles per second, how long does it take the speed of light to get from the sun to the earth? Show me the answer in minutes.

Green a/c units [ 2 Answers ]

I'm looking for a residential a/c unit that is green friendly can you suggest one

Using units [ 5 Answers ]

turning kg into joules do you use the units kilograms when working out an equation or would you convert them into g before using the equation

Converting units [ 3 Answers ]

Hello :) How to convert microliters into micrograms?? I know it shoul be easy, but tell me how :) Tnx

Matching A/C units [ 7 Answers ]

Do I have to match the outside unite with the inside unite? I have a Rudd sys. Right now the heat pump outside is gone out. Do I have to replace with the same brand or can I go with an other brand? I'm in Dallas/Ft. Worth Tx. Do I need to go back with Heat pump or can I just go back with a a/c...


View more questions Search