    Do I need an Electrical Subpanel?
    I have a 200 amp panel that is aluminum wiring. I had an air conditioner installed, and although it is on it's own breaker, it blows the main, not it's own breaker. It runs for a short time, but it always pops the main, even if almost nothing else in the house is running. Do I need to replace the main breaker, or is the problem more serious?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 14, 2007, 03:23 AM
    I think you will find that there is a loose connection either on the line or load side of the breaker. Loose connections tend to heat the metal connector and wire, and the heat is transmitted or conducted into the breaker. Breakers have a thermal component to them and will trip when enough heat is sensed.

    It is possible the breaker is defective, burnt or dirty contact surfacer inside can raise the resistance of the contacts and again created heat.

    You may try tightening the lugs holding the wire, be sure to tighten the lugs to the breaker also. I had found a nut bolting a breaker tab to a bus bar in a 200 amp GE residential panel, only had 20 amps on it, and it was loose enough to create enough heat to trip the breaker. I found this using an infrared detector, with only idiot lights. Nowadays I use a real Flir infrared camera to find hot spots caused by loose connections.

    Working on the line side of the breaker will require the line to be shut off. This usually is done by pulling the meter. Once the line is de-energized at the breaker, then all the connections can be checked. Each lug and wire connector will have it's own torquing spec.

    If the connections are not the problem, the breaker may need to be replaced. This can be confirmed using a millivolt tester, or a low resistance ohm-meter. Either can be used to detect high resistance at the contact points.

    None of this is really is for a DIY'er.The utility may be needed to pull the meter, this is something a DIY'er should never tackle. The connections will require a torque wrench or torque screwdrivers. And the test instruments are expensive. Anything less than using the proper equipment will be guessing.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical Subpanel [ 1 Answers ]

I have used all the breaker positions in my existing electrical panel. I want to install a subpanel right next to the present one. Are there any code requirements about spacing?

New electrical subpanel in firewall [ 2 Answers ]

I am in the process of building a 14x18' additon and a 24x30' garage (the addition is between the garage and existing house). My existing electrical panel (200 Amp), while having plenty of spaces for all of the new breakers I will need, I have decided to install a new subpanel in the garage as...

Electrical subpanel in fire wall... is it OK? [ 2 Answers ]

I asked this in the electrical section but was refferd here... I am in the process of building a 14x18' additon and a 24x30' garage (the addition is between the new garage and existing house). My existing electrical panel (200 Amp), while having plenty of spaces for all of the new breakers...

Electrical Subpanel [ 1 Answers ]

I want to install a electrical subpanel(~50 amp) in my garage, if I do not feed the subpanel with a breaker from the main service of the house,would or could I tie into the main lugs of the main service to feed the subpanel? (Using the proper wire size) Would I have to use a ground rod for the...

Grounding a subpanel [ 1 Answers ]

I have a set of direct current solar panels mounted on a metal structure (carport). All the panels and the structure are grounded to a ground rod driven near one of the support posts. Can I use the same ground rod for the ground connection of an alternating current subpanel mounted on one of...


View more questions Search