    Wire Gauge and Amperage
    If the wire gauge to a machine is changed, will the voltage/amperage to the machine automatically change? Or does it matter what the machine actually uses?

    In my case, the amperage was already much lower than the original wire gauge, but now the wire gauge will match better with the actual usage.

    Thank you!
    Capuchin's Avatar
    Capuchin Posts: 5,255, Reputation: 656
    Uber Member
     
    #2

    Jul 12, 2007, 04:45 AM
    Hi, this has nothing to do with energy, please take care to place your questions in the correct forum in future. Thank you.
    I am getting a moderator to move it for you now.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Jul 12, 2007, 05:46 AM
    Are you talking about reducing the size of wire, smaller than the manufacturer?
    Or are you talking about wire in machine smaller than wire feeding it?
    There is also starting current. What is machine?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Jul 12, 2007, 06:04 AM
    As long as the wire size is still adequate, the machine will still draw the same amperage and the same voltage. If the wire is undersized, the voltage will go down and the amperage up. And yes you need to allow for start up.

    Once when I specified #14 or larger for a pump drawing about an amp, a nitwit in purchasing told me #14 wasn't large enough for 480 volts.
    syarring's Avatar
    syarring Posts: 2, Reputation: 1
    New Member
     
    #5

    Jul 12, 2007, 11:17 AM
    Quote Originally Posted by Stratmando
    Are you talking ... What is machine?
    My question was for the supply power to my machine.
    The machine is a radio frequency sealer.
    I think the actual usage is around 40 amps at start-up of the cycle (208 vac 3-phase power).
    Of two identical machines in my plant, one is supplied with #2 wire, 100 amp breaker, and the other is supplied with #6 wire 60 amp breaker.
    edtech87's Avatar
    edtech87 Posts: 5, Reputation: 1
    New Member
     
    #6

    Sep 23, 2010, 08:38 AM
    The circuit breaker is there to protect the wire, not the equipment. If there is a fault in the feed to the machine or in the machine itself, the breaker is in place to prevent the fault from causing your wire to catch fire and burn your building down. The breakers mentioned above ( 100A for #2 and 60A for #6 ) are properly sized to prevent faults from overheating them. Beyond that, machines that operate on less than, or more than the specified voltage do not operate efficiently and will fail prematurely. Typically, rotating machines have large start currents and may need to step down the wire gauge so the voltage does not drop excessively.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Sep 23, 2010, 09:14 AM

    Ed,

    This thread was opened in 2007.

    Because of the new skin, we have to be careful about answering dead items. :)
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Sep 23, 2010, 09:23 AM
    I know this is an old thread.

    However, a new answer, that I must comment on:


    Quote Originally Posted by edtech87 View Post
    may need to step down the wire gauge so the voltage does not drop excessively.
    Step down the wire?

    Confusing advice.

    I would say step up, if I had to use the same terminology.

    Better said, increase the wire size to reduce voltage drop.
    edtech87's Avatar
    edtech87 Posts: 5, Reputation: 1
    New Member
     
    #9

    Sep 23, 2010, 09:56 AM
    Comment on edtech87's post
    When I wrote step up wire gauge it looked wrong, so better said it should read "increase wire size" instead of "step down wire gauge". The problem is misunderstanding the function a fuse is suppose to perform.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Sub panel feed wire gauge [ 1 Answers ]

I am adding a sub panel to a new garage addition. New 125 amp panel with a double 50 amp breaker in the existing panel. The new sub panel will be 75 feet from the existing main panel. My concern is the correct wire gauge because of the length of the run. The cable will be inside underfloor then in...

14 gauge wire on 20 amp circiut [ 1 Answers ]

Can I use 15 amp outlet on 14 gauge wire that goes into a split box that has 12 gauge wire that goes back to the fuse panel and has a 20 amp circiut

Gauge of wire? [ 1 Answers ]

Thank you for responding. I would like to know what size of wire I need to run a circuit 125 amp, 240V to a sub panel 244 feet away? Or, what size of wire I need to run a circuit 60 amp, 240V to a sub panel 244 feew away? Thank you in advance

Mixing wiring and outlet wire gauge . [ 5 Answers ]

If I have a 15 amp circuit, and 14 gauge wire, why can't I install a 20-amp outlet? If a 20-amp device is plugged into the outlet, won't the circuit trip, preventing overload? Also, 20-amp outlets and 15-amp outlets appear to have the same connection for devices (two prongs and a ground hole),...

Wire gauge drop for lights? [ 1 Answers ]

I'm installing two sconces over a sink, each will have a 60 watt maximum bulb. The switch will share a box with the GFCI that is on a dedicated 12 gauge 20 amp circuit. Can I use 14 gauge wire from the load side of the GFCI to power the switch and then run 14 gauge to the sconces or must all...