    15 amp outlet on 20 amp circuit
    Can I use a 15 amp outlet on a 20 amp circuit. Wire with 12 gauge wire.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 30, 2007, 03:30 PM
    Yes.
    ElecPro81's Avatar
    ElecPro81 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 20, 2011, 05:25 AM
    15amp outlets are made for 14 gauge wire. The 12 gauge wire of a 20amp circuit may not fit into a 15 amp circuit. Properly or take more time to install. Cost of a proper 20 amp outlet is low. Be sure to pigtail outlets: do not wire through the outlet by connecting the outlet in between the two cables of a run because all the current in the circuit then runs through the outlet. A 15amp outled wired incorrectly in this regard would be even more susceptible to overheating, burning up, causing a fire.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jul 20, 2011, 05:32 AM
    15 Amp receptacles are allowed by Code, and are designed to connect to 20 Amp circuits with #12 wire.

    While pigtailing is better method, receptacles are designed and listed for feed through.
    ElecPro81's Avatar
    ElecPro81 Posts: 2, Reputation: 1
    New Member
     
    #5

    Jul 20, 2011, 08:55 PM
    Comment on tkrussell's post
    Regarding feedthrough connections: I have had to repair several house circuits which were wired feedthrough, replacing all the burned outlets on circuit. Cutting back burned & arcing #14 wire. (Never with #12) Also replacing burned up 15 amp breakers. The homeowners were using trial & tripout to load the 15amp circuit to just below it overloaded, for prolonged times. This is not a rare event in my experience, particularly with heavy electronics plus heaters, water cooler, & small refrig or freezer. (despite my severe tongue lashing of homeowners) In addition, the outlets had the wires pushed into the back rather than more securely connected with screws, which I believe contributed to the problem. Common fast lazy installation method. I disagree about using #12 wire with cheap (or older) 15amp outlets. Cheap outlets are hard to wire with #12, & holes in back are too small to push #12 into. You are using quality materials & wiring correctly so no problems like this!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Jul 21, 2011, 12:59 PM
    Quote Originally Posted by ElecPro81 View Post
    15amp outlets are made for 14 gauge wire. The 12 gauge wire of a 20amp circuit may not fit into a 15 amp circuit. properly or take more time to install. Cost of a proper 20 amp outlet is low. Be sure to pigtail outlets: do not wire through the outlet by connecting the outlet in between the two cables of a run because all the current in the circuit then runs through the outlet. A 15amp outled wired incorrectly in this regard would be even more susceptible to overheating, buring up, causing a fire.
    This is completely incorrect.

    Unless you are in Canada, using 15A recweptacles on a 20A circuit is ABSOLUTELY FINE.

    I am not sure where you are getting your information from ElecPro81, but 15A receptacles ARE rated for 20A feed-thru.

    Also, #12 is no harder to work with as far as receptacles go. There is NO DIFFERENCE when using the side screws as most real electricians do. Yes, receptacle "back-stab", or quick-wire, connections are no longer rated for #12. This is an age old problematic issue which is why almost no one uses those connections on devices.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

20 AMP Circuit with 15 AMP Receptical, is this OK, and in code? [ 5 Answers ]

This is sort of similar to the other thread, but my problem is the house I bought is wired with 12, all the breakers are 20AMP except for the 30AMP for the AC and Dryer. When me and my dad were changing the power recepticals, which were 15 amp, someone told us that we should have 20 recepticals, or...

Can you use a 15 amp outlet on a 20 AMP breaker with 12-2? [ 13 Answers ]

I have a few questions that I need help on. I recently moved into my home and discovered a few things. 1. 12-2 wire has been ran throughout the house. Can you use a 15 amp outlet on a 20 AMP breaker with 12-2?? 2. How many lights would you say you can run on 12-2 and/or 14-2 wire? 3. How...

20 AMP Outlet on a 30 AMP Circuit [ 7 Answers ]

I have a question regarding putting a 20 amp outlet on a 30 amp circuit. I'm replacing appliances in my kitchen, and there's currently a 30 amp, 240V, 3-wire + ground feed to the location where the oven is located, on a 30 amp, double pole breaker. I'm planning to install an electric oven (240V)...

20 Amp outlet. Have an a/c with 15 amp plug [ 1 Answers ]

I have a big problem in that my window is less than 26 inches wide. I need a 24,000 BTU air condtioner. The only AC I found is a GE ASM24DK. It has a 220 volt 15 Amp Perpendicular plug. The problem is that I have a 220 outlet, but the plug type seems to be a 20 amp. The top of the outlet has a...

Compatibilities between awg wiring, breaker amp size, outlet amp size [ 4 Answers ]

Hi. Is there a resource out there, prefereably on the web, that outlines the compatibilities between awg wiring, the breaker amp size, outlet amp size, how many recepticles/outlets can be on x amp outlet, etc? For example, it would be nice to see something that shows: you can use a 20 amp...


View more questions Search