    Home A/C heat pump freon amount.
    I have been out of the business for 20 yrs and I didn't keep any of my books on A/C.
    For a 3 and one half ton central air heat pump (Trane) totally evacuated system about how many pounds of Freon will it take. I am talking pounds by a scale from a 30 lb can of R22. Depending on the outside temp and other things the gauges may not be right. The old timers use to weigh their cans before and after. One reason was to charge so much per pound for a service call but the other reason was to see if too much Freon went in or not enough on cold days. So what I need to know is about how many lbs approx should my unit hold .
    I am thinking 6-8 lbs. IS 8 pounds too much? How much is to high of pressure on the low side? I am getting 58 degrees out of my registers. What happens when too much Freon is in the system. Will the condenser freeze up?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Apr 27, 2007, 07:31 PM
    You can weigh in the amount by looking at the model tag on the unit. Usually it is listed there BUT to be honest it is not that accurate. You will need a good quality set of gauges and thermometers and then charge to Superheat or Sub cooling depending upon your metering device.
    I am sure you are certified because the EPA has a 25,000.00 fine for all the folks who are not certified for handling refrigerant. Good luck.
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #3

    Apr 27, 2007, 08:05 PM
    The total amount will also depend on the length of your line set and what size liquid line drier you use. Just as hvac1000 said, using superheat and subcooling readings is the only correct way to charge your system. Also don't forget to use a bi-flow liquid line filter drier for your heat pump.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #4

    Apr 27, 2007, 09:03 PM
    I would assume that you don't know how to use subcool and superheat otherwise you wouldn't be asking, I would say depending on your lineset for a 3.5 ton 8 pounds would be a little much... wait until the house gets good and warm, add what the name plate reads and get a 15 to 20 degree split, that should be close. At 75 in the house don't allow your suction press. To get over 70. Like hvac1000 said if you are not EPA cert. I wouldn't touch it, it would cost you a lot less for a service call then a fine!
    curtismiller's Avatar
    curtismiller Posts: 1, Reputation: 1
    New Member
     
    #5

    Apr 9, 2011, 08:21 PM
    How much liquid goes into a unit that calls for 6 ,6 pounds after a compressor change

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

Heat pump stuck in heat mode [ 4 Answers ]

I have a heat pump that seems to be stuck in heat mode. When you try to turn the a/c on it runs heat. I got the a/c to run by cycling the power a couple of times but after having to use the heat again, it is stuck again. Could this be an electrical problem or is it probably the reversing valve?

Electric heat pump auxilery heat problem [ 4 Answers ]

Equipment: Trane XL1400 4 years old Auxilery heat: Strips... 2 -60Amp circuits Filters changed every 30 days I cleaned outdoor unit summer 2006, as every year. Thermostat: Honeywell Chromotherm II Problem: I have been noticing at times the aux heat kicking in at times I think it should not....

Heat pump vs electric heat [ 3 Answers ]

I have a heat pump with a two stage thermostat, 1st stage is heat pump, 2nd stage is electric (resistance) heat. Is it ever more economical to run the furnace with resistance heat only, not the heat pump? I know that the outdoor temperature affects the ability of the heat pump to work, but is...

Home Heat pump Inop [ 1 Answers ]

  My home heat pump compressor stop spinning.  The pump is controlled for air conditioning and heat from a central thermostat in the house.  The fan works OK and you can hear a click sound at the heat pump when the thermostat is turned on.  The house and system circuit breakers (fuses) are on. ...


View more questions Search