    AC condenser fan turning on and off intermittently
    I just turned on the AC for the first time this season and I noticed that the condenser fan outdoors is continuously turning on and off intermittently, i.e.. on for three seconds, off for three seconds; on for three seconds, off for three seconds, etc. This is a Carrier unit. Any idea on how I can repair myself or should I put up a service call?
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #2

    Apr 27, 2007, 02:11 PM
    Not an easy solution from where I sit. It is a very unusual problem and might need some trained eyes at the unit to figure it out.
    Good Luck
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #3

    Apr 27, 2007, 03:02 PM
    Is the compressor shutting off as well? Or just the cond. Fan?
    racednav's Avatar
    racednav Posts: 4, Reputation: 1
    New Member
     
    #4

    Apr 27, 2007, 04:03 PM
    The fan on the compressor outdoors is all that I am noticing that is shutting off.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #5

    Apr 27, 2007, 09:35 PM
    Well it could be that maybe it is going out on overload, but it would stay off longer. There isn't any type of fan cycling device on the unit? Does it act like it has any trouble starting back up? Is this the first time that you have heard this system run? If so it sounds to me like it has a low ambient control on it, therefore that is normal...
    racednav's Avatar
    racednav Posts: 4, Reputation: 1
    New Member
     
    #6

    Apr 28, 2007, 05:14 AM
    This is the first time that this has occurred. I've had the system for seven years and never had this problem. There is no indication that it has trouble starting back up. I have a service technician from the hvac company that originally installed the system coming on Monday afternoon. I'll let you know what he/she comes up with. Thank you for your help.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #7

    Apr 28, 2007, 09:05 PM
    Is it a R22 or R410 refrigerant system? Top of the unit above the freon lines is a rating plate.It will tell you how much and what type of refrigerant you have(out side unit). The R410A unit has a pressure switch that will cycle the condenser fan motor it may be going bad or low on refrigerant will also do it. Give us more info if you can.
    racednav's Avatar
    racednav Posts: 4, Reputation: 1
    New Member
     
    #8

    Apr 30, 2007, 08:13 AM
    It is a R410A system. The hvac technician said that it had a valve stem leak which caused it to be low on refrigerant, which caused the low pressure control switch to make the fan run intermittently. All set now. Thank you all for your help.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #9

    Apr 30, 2007, 09:58 AM
    Quote Originally Posted by racednav
    It is a R410A system. The hvac technician said that it had a valve stem leak which caused it to be low on refrigerant, which caused the low pressure control switch to make the fan run intermittently. All set now. Thank you all for your help.
    Most A/C's use the low pressure switch to open the low voltage on the contactor, so when it tripped on low pressure the entire unit shut down, not just the fan. I realize most homeowners don't quite understand fan from compressor, but that would be very useful information for us online to know. I'm simply putting this post here in hopes that others with similar problems will read it.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #10

    Apr 30, 2007, 04:32 PM
    Carrier\Bryant has a vapor pressure switch that cycles the condenser fan motor. They also have the low pressure and high pressure switch that are in the low voltage side to open the contactor.
    hvacstudent07's Avatar
    hvacstudent07 Posts: 1, Reputation: 1
    New Member
     
    #11

    May 3, 2007, 05:09 PM
    Quote Originally Posted by racednav
    I just turned on the AC for the first time this season and I noticed that the condenser fan outdoors is continuously turning on and off intermittently, ie., on for three seconds, off for three seconds; on for three seconds, off for three seconds, etc. This is a Carrier unit. Any idea on how I can repair myself or should I put up a service call?
    You want to turn that unit off and not use it until fixed ,can cause major problems to unit ,although that problem is not hard to fix will get back to you in a bit with what it is. Let me look in notes
    stdenis799's Avatar
    stdenis799 Posts: 2, Reputation: 1
    New Member
     
    #12

    May 29, 2013, 06:43 PM
    Carrier air cooled unit

    Condenser fan runs fine and then goes off when compressors kick in

    Can't get both to run together

    Off course compressors will also stop on thermal shutoff I guess

    Any ideas what's up

    Changed freon filters both compressors c 164 s

    Freon cked again after 164 installed today

    Thanks
    Rob
    [email protected]
    WillieNAz's Avatar
    WillieNAz Posts: 1, Reputation: 1
    New Member
     
    #13

    Jul 14, 2015, 10:00 AM
    My Carrier technician bypassed the thermostat and saw that there was 120VAC going to the fan motor and also saw that 24VDC was present at the motor and it still kicked off even though it was still calling for the 24VDC and the voltage was still present. He said the fan motor has a circuit board built into it so the circuit board was bad and he needs to replace the motor. Seems like a silly design to not have the circuit board separate from the motor, but at least mine is under warranty. Hope that helps others who may have the same issue. Measure the voltage going into the Molex connector near the top of the blower and see if the 24VDC is still there when the fan stops blowing... if it's still there then the circuit board built into the fan is the problem.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Fan motor intermittently stops [ 2 Answers ]

I found the problem when my ac lines froze... I checked the filter and A coils for dirt restricting air flow... all was clear. I then noticed when the ac unit is running the fan would quit running will the AC unit continued running. I then shut the air off and set the thermostat to fan ( so the...

Condenser fan [ 2 Answers ]

Hi everybody My condenser fan stop working, the ac guy came to fix it but I noticed that he installed a two blade fan instead of three blade that was before. Will it make adifference in performance of condenser ? Thank you I will apreciate your answer John

Condenser fan [ 1 Answers ]

I have a ac/heat pump. I used the heat pump the other night. The disired temp was reach, but the condenser fan will not shut off unless I turn it off at the breaker. Could this be a relay issue or thermostate issue?

Compressor fan works intermittently [ 10 Answers ]

The compressor fan for my AC (Central Air) unit (that is located out side of the house) works intermittently. The fan comes on for few seconds and then turns off. Sometimes I can hear some noise from the compressor unit before the fan turning on. Any help is highly appreciated. Best...