    Heat Pump (A/C)
    In the early AM when the unit tries to come it just humms and the fan doesn't move. I have replaced Fan motor and blades. Could it be the wiring in the unit outside or could it be something inside the house? Thanks in advance for any suggestions.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Apr 23, 2007, 10:00 AM
    Could be many things. Start with checking both high and low voltage circuits. Then see if the contactor in the outside unit is working.
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #3

    Apr 23, 2007, 01:36 PM
    If the compressor hums and tries to start and the fan won't run, you may have a bad dual run capacitor. Sometimes a completely open run capacitor will keep both from starting. Other than that it could be a lot of things.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

NO HEAT! Janitrol heat pump and AC system. Changing to Lux Thermostat. Wiring issue. [ 11 Answers ]

I have a Janitrol A/C and heat pump system. I replaced the thermostat with a Lux T9000LC The A/C works fine, but the heater does not. I have it wired as follows: G - Green Y - Yellow W - White RH - Pink B -

Electric Heat-Pump-No heat [ 2 Answers ]

I had a wall-mounted unit installed in a room in may of this summer. In the middle of the night the heat shut off and has not come back on since. It is an Amana, electric heat with heat pump unit. The cooling works, the heating setting does not blow air at all. When I remove the cover it says...

Heat pump stuck in heat mode [ 4 Answers ]

I have a heat pump that seems to be stuck in heat mode. When you try to turn the a/c on it runs heat. I got the a/c to run by cycling the power a couple of times but after having to use the heat again, it is stuck again. Could this be an electrical problem or is it probably the reversing valve?

Heat Pump - Emergency Heat [ 2 Answers ]

My heat pump keeps changing itself to the aux heat. Can you tell me why it is doing this and how I can prevent it from doing it.

Electric heat pump auxilery heat problem [ 4 Answers ]

Equipment: Trane XL1400 4 years old Auxilery heat: Strips... 2 -60Amp circuits Filters changed every 30 days I cleaned outdoor unit summer 2006, as every year. Thermostat: Honeywell Chromotherm II Problem: I have been noticing at times the aux heat kicking in at times I think it should not....