    will6000's Avatar
    will6000 Posts: 1, Reputation: 1
    New Member
     
    #1

    Nov 24, 2015, 10:51 PM
    Lost half my zones, no breakers tripped, can turn back on zones by turning on my oven
    I was attempting to fix a wall sconse. It worked when I bought the house but stopped shortly later. I fixed what appeared to be an old loose wire, and upon hitting the switch power went off in about a third of the zones in the house.


    Now I've tried to figure out the cause of this because no breakers were tripped when it happened. I used a volt meter and tested the legs to the house and the one reads 120v when I test it with the ground wire.


    Now here's where it gets weird. My 220v oven when set to broil will cause the lights to come back on in parts of the house though the volt meter reads that they're only getting about 94v. I can control several lights by using my oven dials.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Nov 25, 2015, 04:43 AM
    You have lost one of the two hot leads coming into the house. What is happening is really not weird. When you turn on the oven, which is connected to both hots, power passes through the element from one hot to the other.

    First try resetting the main breaker. That's not likely to be the problem but try anyway.

    If you feel competent, remove the panel cover and do a voltage check between the lugs of the service entrance cable. Should read 240V between lugs and 120V between each lug and the ground or neutral.

    Then call power company.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Nov 26, 2015, 07:02 AM
    "and tested the legs to the house and one reads 120v"
    What about the other one? You need two 120v legs for a complete service (at least).
    You found your problem... now you need to find out what caused it.
    Call the power company.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #4

    Nov 27, 2015, 08:27 AM
    This is a symptom of what happens when you lose the neutral, either in a circuit or the main service. Immediately call a licensed electrician to investigate. This condition can cause significant damage if it has not already....
    Please write back and let us know what you found out!
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Dec 4, 2015, 11:05 AM
    Tempted to believe 1 Hot was lost as well. A Breaker may have been tripped, but not thrown. A Bad breaker, Burnt or corroded buss could do as well.
    You need to test for not just 120 volts to Ground/Neutral, but for 240 volts between the 2 hots. This is probably fixed by now.

    Ran into a strange one one time, Owner said they heard a loud POW, everything went off, then Back on except 240 Volt stuff. I had 120 volts off each hotleg at the Panel, But Zero volts between the 2 hots(should have been 240 volts), Went to outside Disconnect and had 240 volts between both legs, I told owner somehow it appears that the 2 hots between the Disconnect and the panel have fused together and blew open 1 leg coming from the disconnect, but were joined together in the underground aluminum conduit. Had an LB at ground level, And had to use a Heavy Duty Utility Truck to pull the Conductors out which had also melted to the Conduit. That was strange.
    If a hot leg is lost, you may still see 120 volts one each leg, but zero between the 2.
    Curious what was the result. Take Care

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

All zones come on when one is up [ 2 Answers ]

4 zone gas heat... Moved thermostat and now all zones are acting as if on one thermostat n the automag board connections r reading right... All 3 wires are connected on the oolder thermostat... The zone moved seemed to get the most heat though... Don't know?

No heat in 2 zones [ 0 Answers ]

I recently renovated a home and installed a new weil mclaen high eficiency boiler with 5 zones. 2 zones continue to shut down. After purging they work for a few days to a week and then they shut down again. No visible leaks anywhere. Recently we discovered that the pressure relief valve was bad....

?No heat through both zones. [ 0 Answers ]

Have a two zone heating system and both not working. AT first only 2nd floor was getting heat. Someone suggested replacing the circulating pump. I changed it, bled the pipes and now both zones are not getting heat. What can be the problem?

1 out of 3 heating zones not working [ 3 Answers ]

Our heating system seems to be operational... specially given the fact that 2 out of the three zones work like a charm. The zone that doesn't work uses a "Honeywell V8043 E 1012 motorized valve", and since the problem started, we've replaced the motor only... and it didn't work. Now, we've...


View more questions Search