Ask Experts Questions for FREE Help !
Ask
    midas28's Avatar
    midas28 Posts: 3, Reputation: 1
    New Member
     
    #1

    Aug 11, 2015, 09:05 AM
    New HVAC Coil Problems
    Hi
    Our Carrier HVAC unit's coil was leaking water over our basement floor. For about $700 we had it and the pan replaced. The tech charged it back up and it worked great for about 24 hours. Then it started to barely push air and that air was not cool I called the company. They came out and said the original tech didn't charge the unit enough (since it was an older unit it needed more than the industry standard)
    He charged it and it worked great for about 48 hours. Now the same thing is happening. While water was leaking on our basement floor, it worked fine before the new coil. I have to call them back, but I wanted to be somewhat knowledgeable. It just seems a bit suspicious that now that we have a new coil it isn't working correctly. Is there any reason this would be happening---incorrect installation, incompatible parts, etc.

    Any thoughts would be appreciated.

    Thanks!
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Aug 11, 2015, 10:42 AM
    Did 2nd tech check the first techs soldering for for refrigerant leaks?
    midas28's Avatar
    midas28 Posts: 3, Reputation: 1
    New Member
     
    #3

    Aug 11, 2015, 11:45 AM
    No he didn't. I don't understand the terminology but he said the first tech only filled the refrigerant up to "11" and because it was an older model it needed to be charged to "17". He thought that would do the trick, but it only seemed to do so temporarily.
    Thanks
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Aug 11, 2015, 03:10 PM
    Sounds like a coil leak to me. Unless you have a 5 ton+ unit with a very long lineset, 11-13 # is about average. 17 seems like a lot.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #5

    Aug 12, 2015, 08:25 AM
    Our Carrier HVAC unit's coil was leaking water over our basement floor.
    That probably occurred because the pan under evaporator coil rusted away.
    When air is cooled the moisture in the air turns to water. The pan under the coil catches the water and lets it drain out a condensate pipe to an acceptable place.

    When the part of the system outside compresses the freon gas it makes it release the heat. When the freon comes back inside and the pressure is released, it expands and absorbs heat. That is how the system works.

    In order to replace the rusted out pan, the first tech replaced the part inside where the freon expands. To do that, he cut the tubing that takes the freon outside. He put in the new part, called an evaporator coil (with a new pan). To do that he soldered the tubing to the new coil.
    He then put the freon back in the system. You have to put the correct amount of freon in the system. If you put too much the freon it can't expand and absorb the heat. If you put in little freon, it will expand too much. If it expands too much the moisture in the air will turn into ice, not water. This ice build up will block the air flow.

    Properly charging a system is not easy. There is no certain amount of freon used, it all depends on how big the system is and how long and big the tubing between the inside and the outside is. Charging the system is done by measuring the pressure and the temperature.

    When you solder pipe or tubing, you sometimes have a leak. If the first tech properly charged the system but had a leak, the system would run for a period of time. But as the freon leaked out, the system would have to little pressure and ice would form, blocking the air flow.

    If the second tech just recharged the system and didn't check for leaks, he is not to bright. He put more freon in but it has leaked out just like before and the same thing has happened.

    Call his boss.
    midas28's Avatar
    midas28 Posts: 3, Reputation: 1
    New Member
     
    #6

    Aug 12, 2015, 01:32 PM
    Awesome. Thank you. They are coming out Friday morning. Now I can sound somewhat knowledgeable and insist they check for leaks.
    While it is a rather large HVAC company that has been in business for a while, it was the Service Manager who came out Saturday morning and didn't check. Makes me not have a lot of confidence in them.

    Thanks again to everyone!
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #7

    Aug 12, 2015, 02:07 PM
    When they are charging, watch the gauges. Look up AC head pressure on Google and It will give you the ranges and ambient temps for 22 and 410A.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hvac problems [ 0 Answers ]

Customer called and said the a.c wasn't working I went to the roof and the liquid line had oil around it the fan motor was spinning very very slow so I checked the compressor and it was defected. The contactor was stuck. I bought an entire new condensing unit and replace the old one. Now the unit...

Coil problems [ 2 Answers ]

How long should the coil last before rusting out

2009 ieec hvac code compressor/evaporator coil changeout [ 0 Answers ]

I will be changing out my system to a new compressor and evaporator coil, a new plenum will have to be built is there anything in the energy code that says that all of the ductwork will have to be brought up to code or that the system will have to be pressure tested? I am looking for anything code...

HVAC - Freon and/or Coil Issue [ 1 Answers ]

Our HVAC wasn’t blowing cold air a few weeks ago. It was out of freon, so we had it filled. Now, the system stops blowing air (although everything is on) after its been on for a couple of hours. Our HVAC guy says that there’s likely a Freon leak and the coil is likely freezing up. He wants...

HVAC coil restriction [ 1 Answers ]

I have an 8 year old Trane dual heat unit and a 6 month old Amana 5 ton Heat Pump which replace an 18 year old heat pump. The electric consumption has increased since the new Amana was installed and it was supposed to be more efficient. In November the service technician found head pressure of...


View more questions Search