    Traveler wire
    Can a length of stranded 14 gauge wire be used as the traveler along with 14-2 with ground when wiring 2 LED light fixtures in the kitchen? I both on hand and do not have 14-3 with ground.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Jan 12, 2015, 08:03 AM
    No. To say it simply, all conductors must be in the same sheathing.
    Kitchen2015's Avatar
    Kitchen2015 Posts: 3, Reputation: 1
    New Member
     
    #3

    Jan 12, 2015, 11:05 AM
    Thanks for the answer- Could I get some clarification- by in same sheating - is that meaning all wires must be in the same bundle of romex- i.e. 14-3 with ground romex and not romex and a strand wire? If not can I use 2 lenghts of 14-2 with ground romex and use just one wire out ot the second romex length as there traveler. I don't want to buy a roll 14-3 if I can do it safety with the 14-2 wire I have.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Jan 12, 2015, 12:49 PM
    If not can I use 2 lenghts of 14-2 with ground romex and use just one wire out ot the second rome
    No.

    All conductors must be in same sheathing (outer covering) or conduit. Meaning same bundle. That ensures that all conductors are parallel to one another and in close proximity to one another.

    The reason,
    An electrical current in a conductor has a magnetic field surrounding it. With AC current that magnetic field is constantly expanding and collapsing. That expanding and collapsing magnetic field will induce a current in any conductive material within its range. That means a conductor run by its self, next to something like a water pipe can induce a current in the water pipe even though there is no direct contact.
    Therefore, the neutral wire must be in the same sheathing or conduit as the hot wire. While the hot will create a magnetic field in one direction, the neutral will create an opposite magnetic field because the current is traveling in opposite directions. The two cancel each other out.

    There are five ways to wire a set of 3-way switches.
    The first is to feed switch one and use the traveler wires to switch two and wire from switch two to the fixture.
    When wired this way the neutral runs with the hot travelers. The neutral cancels the magnetic field around the hots no matter which traveler is being used.

    With all other ways of wiring a set of 3-way switches one of the two travelers legs takes the current from switch 1 to switch 2. The third common leg takes the current from switch 2 back to the box that contains switch 1. There it is connected to the hot going to the fixture. Therefore you have a magnetic field in one direction on one of the traveler legs, and an opposing magnetic field around the common traveler. Again cancelling each other out. For that to happen the conductors must be parallel and adjacent to one another. So NEC code says same cable.

    With DC current you don't have to worry about this. DC current has the magnetic field surrounding the conductor but it is constant. It is the expanding and collapsing of the magnetic field that induces the current in another conductor.

    You should be able to buy 3-wire Romex by the foot at Home Depot or Lowe's. If not come by my house and I will give you some.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

1st time traveler out of Ghana [ 3 Answers ]

Do they need to show 4000.00 before they travel

Ok, maybe he's a time traveler [ 1 Answers ]

This guy comes to this planet. He wants to be helpful. He says he is looking for great danger. Or something like that. He runs into this pimp or drug dealer or all around bad guy. The guy says something like; "I'm looking for great danger" and the bad guy says "You found it all right! Anyway the...

Name of movie? Irish Traveler's [ 2 Answers ]

Kyra Sedgwick and Colm Meaney played in a movie together about Irish Travler's (gypsy's) It was centered around two runaway brothers and a white horse that was supposed to be there reincarnated mother's spirit that help's them. I don't know the name of the movie, can anyone help>:confused:


View more questions Search