    Wire sizing for 550 feet service
    What size entrance cable do I need to run a 200 amp underground service to my house? Meter wii be at the road, conduit is in place. Power company wants 6000. To run power back to the house, 1800. From across the road to a pole I'll have to erect. Another question. Can the pole I install be steel pipe instead of a treated pole?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Nov 18, 2014, 08:36 AM
    You would need to use #500 sized aluminum cable. Also, you need to verify that the conduit you have installed is the correct size for the cable.

    I do not know if the SE comes in 500 cmil size or not, you may have to use three single cables.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Nov 18, 2014, 01:38 PM
    The pole will h ave to meet the utility's spec, so you'll need to ask them.

    As for the cable/wire, why 550' of secondary? Did no one suggest running primary and transformer closer to the house?
    shopteacher's Avatar
    shopteacher Posts: 2, Reputation: 1
    New Member
     
    #4

    Nov 19, 2014, 05:51 AM
    The utility company wants close to $6000 to run the primary to within 120 feet of the house. If I set my own pole at the road and install everything else they'll run 74 feet of overhead to my pole for $1800
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Nov 19, 2014, 11:37 AM
    Quote Originally Posted by shopteacher View Post
    The utility company wants close to $6000 to run the primary to within 120 feet of the house. If I set my own pole at the road and install everything else they'll run 74 feet of overhead to my pole for $1800
    OK, so what do you think will that remaining 476' cost you?
    Where do you live. Most times the customer is responsible for underground wire. The utility might want 6 grand, but an electrician will probably cost you $4-5 grand for the same thing.
    Once you get into the distance you are talking about nothing is cheap.

    Either way, no way I'd run secondary 550'.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Nov 19, 2014, 12:20 PM
    Again, to run 550' you would need to spend close to $3500, before tax and shipping on the cheapest rate I could find on the web.

    Also, your conduit would have to be trade size 4 for RMC conduit or trade size 5 for schedule 80 PVC conduit. Any size smaller would not meet the code standards.

    Stan's suggestion are much better than the costs plus labor plus the costs for renting the proper equipment to do the trenching.

    All of this assumes that the Utility will allow you inside their boxes to make connections at both ends, transformer and meter base.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size wire do I need to run 45amp service from a 50 amp sub panel 230 feet [ 7 Answers ]

I need to get 45 amp service to my RV which is 230 feet from a 50 amp well pump sub panel. What is the least expensive awg copper wire I should use?

What size wire for 220v 100 amp service at 100 feet [ 7 Answers ]

I am running 220v 100 ft to a 125 amp sub panel. A welder would be the heaviest thing used. (around 200 amp welder) what size copper wire would I need running in pvc underground

Wire sizing for 200 amp service with 220 ft. Run. [ 1 Answers ]

I built a new shop, pole building and need to run electric service to the shop. The pole with the transformer and ct meter that I will share with my residence is 190 ft. from shop. Total length of cable from transformer to sercice panel will be 218 ft. I will run this underground in appropriate...

Wire sizing for 250 feet service [ 5 Answers ]

I'm running an underground electrical service (240 volt) from the meter to the house, 250 feet. What would the wire size be and the size of the conduit? The main panel will be 200 amps. I would like to get a price for both aluminum and copper. Thanks

Wire Size for 150 amp service 300 feet [ 1 Answers ]

I need to take electrical service 300 feet to my barn. I want to take a 150 amp service. What wiresize to I use for this effort.


View more questions Search