Flame won't stay lit
Goodman gmh80603an gas valve shut off. First turns on, igniter comes on burner light then after 5 seconds goes out then runs through the cycle again but lights for only a second or two. Cleaned flame sensor still the same problem. Installed new flame sensor same problem, unit is a year old.
|
|
 |
Full Member
|
|
Oct 9, 2014, 02:08 PM
|
|
Sounds like it might be the roll out switch. Do you have a voltmeter?
|
|
 |
New Member
|
|
Oct 9, 2014, 09:25 PM
|
|
Yes I got a voltmeter I'll look through the manual and see if I can find the roll out switch and check it.
|
|
 |
New Member
|
|
Oct 11, 2014, 09:38 AM
|
|
Checked all the roll switches, they are good. Check other switches and did get the furnace to stay on for one heat cycle then it went right back to turning on the gas and shutting it back off without ever butting tue furnace in lock mode.
|
|
 |
Full Member
|
|
Oct 11, 2014, 10:05 AM
|
|
So you aren't getting any flash codes?
|
|
 |
New Member
|
|
Oct 11, 2014, 01:54 PM
|
|
That is correct would make it a lot easier if I would get a code
|
|
 |
New Member
|
|
Oct 11, 2014, 03:40 PM
|
|
Was just down looking over the furnace now I'm getting a pressure switch code. Checked continuity over switch while restarting furnace, got good constant continuity but going to get online and order a new one and go from there.
|
|
 |
Full Member
|
|
Oct 12, 2014, 11:34 AM
|
|
 Originally Posted by cesport
Was just down looking over the furnace now I'm getting a pressure switch code. Checked continuity over switch while restarting furnace, got good constant continuity but going to get online and order a new one and go from there.
The best way to check the pressure switch would be to put one lead of the voltmeter on C of the control module and the other lead on the pressure switch. If you have 24V on both sides of the switch then it's closed and working properly. If you have 0V on one side the switch it's open. If it's open then make sure the inducer motor is running.
|
|
 |
New Member
|
|
Oct 18, 2014, 02:01 PM
|
|
Put the new pressure switch in still had the same problem. Decided to pull out the inducer motor and found 2 birds stuck around the fan. Reducing my vacuum. Thanks for your help
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Gas water tank won't stay lit and flame is blue, like it is starving for air
[ 1 Answers ]
Hi
Our gas hot water tank made a bang noise last Saturday morning. Later in the day we noticed we had not hot water. My husband turned it off and was going to wait 5 minutes to relight. While waiting it made another bang. We turned off the gas and called a gas fitter person. He came the next...
Why won't the flame on my York Dimond 80 stay lit?
[ 1 Answers ]
I turn the heat on the thermostat to the automatic heat position, and the furnace will lite for about 5 seconds then goes out. When I turn the power off and turn it back on, the furnace will once again come on for about 5 seconds then go off. The entire time the fan is running, even when the...
Pilot and main flame won't stay lit
[ 3 Answers ]
I have a Coleman propane furnace in a mobile home. Model MGHA-090ABPQ-05. When I light the pilot and close the door to the flame box, the pilot will go out. If I leave the door open, the pilot will stay lit. If you turn up the thermostat and the main flame lights, there is a strange almost...
Bryant furnace flame won't stay lit after a few minutes
[ 8 Answers ]
I have a Bryant Plus 80 model 395C that is 17 years old. I turned the furnace on this weekend and it starts up just fine. The draft blower starts, the igniter glows, the valve opens and it lights the burners. After it heats up the blower comes on as always. After about 3-5 minutes the burner goes...
View more questions
Search
|