    2 pole switch
    I am running a circuit from a 220 20 amp gfi breaker in my panel out to a post for my pool pump. I plan on running two black 12 wires(solid) and one white 12 wire through sched 40 pvc 18" UNDERGROUND to a 220 switch (What wires get connected to the black screws, Line or Load?) and from the switch to my 220 outlet. The white wire gets connected to the ground screw of the outlet and into the gfi breaker at the panel, correct? As far as bonding goes if I use a metal outdoor box that is grounded do I still have to bond it? If so can I secure a bonding lug to the side of the box and connect it via #8 bare copper to the other bonding wires?
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #2

    Apr 14, 2007, 05:13 AM
    If possible you should run a green wire for the ground, white is for the neutral on 120 volt circuits. The wires from your panel will feed the line side of your switch and the lines to your pump will come off the load side. There are many kinds and types of double pole switches and if it's not marked, you may want to check it with a ohm meter just to be sure. Also made sure your wires are approved for damp locations.
    M21519's Avatar
    M21519 Posts: 8, Reputation: 1
    New Member
     
    #3

    Apr 14, 2007, 02:49 PM
    Thhn is ok for wet locations, right? No problem with the green i can run a green wire to the ground screw of the outlet and into the nuetral hole of the gfi breaker, correct? How would you check the switch with an ohm meter?
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #4

    Apr 14, 2007, 04:48 PM
    THHN is approved for wet locations. With the switch turned off, you shouldn't get any resistance between the screws. When you turn the switch on you should get o.oo ohms between one top screw and the screw below it and the same on the other side of the switch. Do this with no wires attached to the switch.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Apr 14, 2007, 06:40 PM
    THHN is not approved with wet locations. Only if it is dual rated THHN/THWN. Any insulation code letter with W denotes wet locations.

    Tho most THHN is rated dual, there still is straight THHN out in the market.

    Line terminals are always at the top of a switch.
    JackT's Avatar
    JackT Posts: 260, Reputation: 19
    Full Member
     
    #6

    Apr 14, 2007, 07:07 PM
    tkrussell is correct. THHN by itself is only rated for damp locations. I always used the dual THHN/THWN.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring single pole thermostat in double pole fixture [ 3 Answers ]

Hello, I am trying to install a line voltage programmable thermostat into a manual thermostat fixture. The programmable thermostat is Honeywell RLV430. Instruction manual here: http://www.homedepot.ca/wcsstore/HomeDepotCanada/images/catalog/b7867367-6c05-4c82-a97c-648044b91564.pdf The...

One pole of untied double-pole circuit breaker breaks [ 5 Answers ]

I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...

Trying to change a single pole light switch to a single pole swith with a light below [ 5 Answers ]

I have a kitchen light and a basement light that are together in one electrical box, but are on single switches. I purchased a "single pole switch and pilot light" combination so I could see easily if the basement light is on. In the box there is a black, red and white wire. For the single pole...

Need longer pole for fan [ 1 Answers ]

Hi, I just got my fan and realized that because I have a slanted ceiling I need to extend the polr from the ceiling. Are there poles available? I need at least 20" from the ceiling. Will this affect how the fan works?

Embedded pole foundations [ 0 Answers ]

I am planning a cabin for part-time use. Does a pressure-treated, embedded pole foundation save that much over a reinforced footing and concrete block? To be sure of being below the frost line, I like the footing bottom to be about 32" below grade. Your input will be appreciated. Stoker


View more questions Search