    Problem with 208 volt circuit
    While working on a parking lot light, with a multi tap ballast, wired to 208 volts. I get 120 volts from the black to ground, then 120volts from neutral to ground, but nothing from the 2 hot legs. Bad Breaker?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 22, 2014, 05:32 PM
    Quote Originally Posted by willed View Post
    While working on a parking lot light, with a multi tap ballast, wired to 208 volts. I get 120 volts from the black to ground, then 120volts from neutral to ground, but nothing from the 2 hot legs. Bad Breaker?
    There is no neutral in a 208V circuit. A you just calling the white the neutral?
    Did it work before? New installation? Tell us more about this.

    Also, are you an electrician? Someone without the proper experience, licensing and insurance should definitely not be working on parking lot lights.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Sep 23, 2014, 04:04 AM
    Are you sure you are working on a 208v circuit because what you described was a two wire cable being used as a 240v supply, not a 208v.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Sep 23, 2014, 01:20 PM
    Are you sure you are working on a 208v circuit because what you described was a two wire cable being used as a 240v supply, not a 208v.
    Don, many if not most commercial 3-phases systems are 120/208V, as opposed to 120/240V.
    willed's Avatar
    willed Posts: 2, Reputation: 1
    New Member
     
    #5

    Sep 23, 2014, 04:37 PM
    I am a Licensed journeyman sign electrician, insured through the company I work for. Yes it is a 208 volt system, all other lights on the property work are on 208 volts. I was calling the white wire as neutral. That wire is in the head where the ballast is. This is an existing parking lot light, actually 2 poles are not working, all others working.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Sep 23, 2014, 06:10 PM
    Are there fuses in the base of the poles?
    Did you check any lighting contactors?
    Half tripped breakers?

    You're probably getting hot on both legs because of a backfeed through the other poles.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How many amps at 208 volt to supply a transformer to create 480 volt 150 amp [ 3 Answers ]

Power requirements using a 112.5 kva transformer

Can you operate a light fixture rated for 240 volt, on 208 volt single phase? [ 1 Answers ]

I have an old street light that has a multi tap ballast, the only markings that I can read on the wires are 240volt. My system is 3phase 208 volt and I was told that I could get a 2 pole breaker and the fixture would work. Is this the case?

Use of 208 Volt verses 240 Volt? [ 1 Answers ]

Pleas help me with the following. If an electrical device is used for heating purposes with a rating voltage of 240 volts, why does it take longer to heat up when connected at a 208 volt source. It seems to me that the current will be higher than a 240 volts and consequently the heating device will...

Can you run a 208 volt heating panel on 240 volt electrical supply [ 1 Answers ]

I have a baseboard electric heater that is 208 volts. My power supply is 240 volts. What will happen if I try to run m y 240 volt electrical supply to my 208 volt electric baseboard heater?

3 phase 208 volt/120 volt .load [ 1 Answers ]

I am trying to hook up a commercial espresso machine which has a 220 line. My existing electrical box is a 3 phase 208 volt/120 volt. Would this be sufficient to handle this?? Thank you


View more questions Search