    Climetec HVAC Honwywell actuator valve cycling on and off every second?
    Hi, I live in a condo with water based heating and AC. I woke up to a loud ticking or panning noise coming from the AC unit. Unfortunately there is no model number on this unit as the painter sprayed over the tag. I believe its called a Climetec fan coil unit.

    I removed the cover and the noise is coming from a Honeywell VC4011-12 valve actuator which is continuously cycling on and off. I can turn off the AC at the thermostat, or close the manual water valve but no relief.. it just keeps hammering away. It stops when I turn power off to the whole AC unit.

    Is the valve defective? Or could this be a symptom of some other problem?

    Thanks
    Bob
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #2

    Sep 3, 2014, 08:55 AM
    It could be a defective valve, but most likely it's the voltage opening and closing the valve. Check all the connections. Then take the stat off and see if it stops.Then jumper from R to Y and see if the valve opens.
    bobboV's Avatar
    bobboV Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 3, 2014, 04:47 PM
    Thanks for responding bitters. I checked all connections last night and all was good. I was able to take the "head" off the actuator and while I could feel it on there was no cycling. I also heard no clicking from any relays. So I assumed it was the valve. What also bothered me is I found a splice in the wiring last night so it was replaced once already.. and the building is only 8 years old. Fortunately the regular hvac technician for this building was available. Turns out the actuator was defective. Apparently the Honeywell VC4011-12 actuators in these Climetec fan coil units have been failing prematurely. He replaced it with a different make. Both the head and the body. This new actuator has a screw valve whereas the old one just moved up and down. All's good now.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

HVAC system inside blower motor cycling rapidly. [ 0 Answers ]

I have a split hvac system. The problem I have is that the blower motor inside the house cycles on and off rapidly. I had a service tech. come out and look at it, he told me that my unit was too old to replace the resistor. He told me they don't make them anymore. Is this true or is he just...

Replace Expansion Valve on a Ruud HVAC Unit? [ 0 Answers ]

Can anyone give me an ideal how much the average cost to replace a expansion valve on a Ruud HVAC Unit? The part is under warranty

Pump is short cycling and blowing foot valve off. [ 1 Answers ]

I woke up Saturday to no water; checked the pump into house and it was running (did not notice the short cyle at the time) so shut it off and checked holding tank. There was plenty of water but the pvc pipe that has the foot valve screwed into it was off. So let the pump cool down and put pipe...

Gain adjustment in chilled water valve actuator control systems [ 0 Answers ]

How to adjust the gain in the programme for proper operation of actuator of two way valve? Actuator is not modulating the valve according to set tempreture.

Bryant Rooftop hvac unit not cycling properly [ 1 Answers ]

I Have an older Bryant 6-ton rooftop unit model 580c that will run for a few minutes... shut off but will NOT "cycle" back on for heat. You would have to "re-set" by powering off/on at the breaker panel. I am getting a "CODE #6 Inducer Motor Fault" even though motor seems to be functioning OK. It...


View more questions Search