    My outside unit is kicking on and off...
    We just replaced the fan motor and the starter capacitor and it starts running just fine and kicks off and then kicks right back on and about 30 seconds later it kicks of again and kicks right back on. What is causing this?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Aug 5, 2014, 09:45 AM
    Possibly a defective contactor.
    Pull disconnect to kill power.
    Remove cover.
    Check all connections, both high voltage and low voltages terminals for good connections.

    If you are comfortable working around LIVE HIGH VOLTAGE, replace disconnect and set thermostat to call for cooling. Observe but do not touch contactor. Contactor should make and hold a connection. If it makes and breaks, you should be able to see and hear it doing so. If contactor makes and breaks and the blower motor in the air handler is running contentiously, the contactor is likely defective.

    Pull disconnect and check low voltage terminals. Should have 24 volts or more across terminals. Remove low voltage wire and do a continuity check between the low voltage terminals. Inspect high voltage contact points for burned points. Contactor may be single or double pole. If you have 24 volts on low voltage and blower motor in air handler is running the contactor is most likely defective and failing intermitantly.

    If you do not have 24 volts at low voltage terminals you may have faulty control board or relay in air handler, faulty thermostat or defective low voltage wiring between air handler and condensing unit.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #3

    Aug 5, 2014, 04:11 PM
    Could also be a thermal cutout switch.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My outside ac unit is faintly humming and the fan is not kicking o [ 0 Answers ]

Just had capacitor changed last wek there is 220 xurclien current hitting the contactor

No heat , unit not kicking on... rheem [ 4 Answers ]

Hi. My rheem heating unit stopped working. It doesn't turn on. Nothing

Trane outside unit not kicking on [ 64 Answers ]

I have an outside A/C unit that does not do anything, I replaced the thermostat over the winter, the heat kicks on with the furnace no problem, but at the thermostat you hear the click when setting the temperature below room temperature, but nothing happens out at the outside unit. I checked the...

Outside AC unit kicking on in winter [ 3 Answers ]

I have central air, and the outside unit (condenser right? I'm a complete noob) kicks on for about 30 seconds, then stops for 30 seconds, then repeats. This doesn't seem normal. Advice? Thx!


View more questions Search