    #1

    Jul 27, 2014, 07:38 PM
    Panel circuit wiring question
    Got a question for the ELectricians here. I am wiring in a welder into my main panel (200 amp service) (5 foot run) 60 amp dual pole breaker (if I can't do it with that I don't NEED to do it) using 6 gauge copper high temperature teflon double insulated wire to a dedicated dual pole breaker (the welder is a 220v 295amp transformer based a/c stick welder so I need everything I can give it). Problem is my common bar won't accept 6 gauge wire, since I understand the common and ground are bonded in the main panel, is it acceptable, safe and legal. To use a copper grounding lug to terminate this on the ground, or what alternative means do I have to do this.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Jul 28, 2014, 03:39 AM
    for a 60 ampere branch circuit you are permitted to use a #10 awg ground...
    NEC table 250.122
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #3

    Jul 28, 2014, 05:00 AM
    By "common" I assume that you mean neutral. For a 240V circuit there should be no neutral, only 2 hots and a ground..
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #4

    Jul 28, 2014, 05:26 AM
    Yes... thats what I mean. I'm an Electronic Engineer, not an Electrical engineer or Electrician the terminology is not the same in my field.

    I'm a bit confused because the charts I looked at say 10 gauge is insufficient for 60 amps at 240v (what I calculate is the maximum I could use when I need to turn it up all the way, and what the manufacturer recommend it be wired for) and 10 gauge is the max size that fits the ground bar. But thats why I'm asking you guys, maybe I'm looking at it wrong and paranoid about undersizing anything. (I've seen far too many melted wires over the years on too many things)

    I need far more than I could draw off the 30 amp dryer circuit I've used this on since 1975 (at much lower welding currents). In a year or so I plan to put a 100 amp subpanel in my garage and move it out there at that time.(using this same breaker position to feed it).. but I have to weld and gusset a set of I-Beams this week and this is the only welder I have with the capacity to do it. Both my MIG and my TIG are outclassed on stuff that thick. And scratch the TIG because I'm doing this outdoors.

    My panel happens to be three feet from my side basement door that opens into my driveway. I'll just run my welding cables out the door when I use it.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #5

    Jul 28, 2014, 07:34 AM
    10 gauge is the max size that fits the ground bar
    I guess I'm confused. You say you are running a cable for a 240V welder. I assume you are running that cable to a receptacle or to a disconnect and then to a receptacle. Logically that cable would be a two conductor cable with a ground. Your connections would be to a double pole breaker and to the ground buss. Depending on the type of cable the hot conductors would be #6 (larger if you are using Romex). The ground would be # 10. Your ground buss should accommodate a #10 ground wire.

    The neutral buss should accommodate at least a #6 conductor. However, there should not be a connection to the neutral buss.

    the welder is a 220v 295amp transformer
    Does welder specify input amperage. Any welder pulling 60 amps is pretty big, especially for a home owner.
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #6

    Jul 28, 2014, 03:44 PM
    This is a big welder... it will do 295 amps. THey actually did call for a 60 amp connection. I looked inside of the panel another time. The ground isn't an issue after all. There was a free lug on very top of the buss I didn't notice before because I was working on the lower right side and it was up on the upper left side. Right next to the ground that went out to the copper rod and right above the tie bar that ties the busses on the left and right side together. The busses themselves won't accept anthing larger than 10 gauge, but the lug would accept stuff up to the size of the servce entry cable.

    THese are pictures of one just like mine.






    Name:  welder-2.jpg
Views: 71
Size:  18.3 KBName:  welder-1.jpg
Views: 74
Size:  16.8 KB

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I need a electrical circuit wiring diagram with the following items in the circuit. [ 21 Answers ]

I have a question that I need answered. I need the folliwing circuit drawn up and emailed to me at: [email protected], before Wednesday, March 28, 2012. Thanks... It would be greatly appreciated. The circuit I need drawn up and emailed to me needs to include the following items in the...

I have a Murray circuit breaker panel and want to add a circuit for a 3 prong elec dr [ 3 Answers ]

I have an electric 3 pronged dryer that I want to add a circuit for on my Murray Circuit Panel. What kind of switch do I need?

Proper wiring for 240 volt circuits on an unbonded branch circuit distribution panel. [ 2 Answers ]

I recently purchased a home and noticed that the following wiring method was used connecting the 240 volt circuits. The branch circuit distribution panel has 4 wires serving it, 2 hot, 1 neutral and 1 bare stranded ground and a solid copper ground wire grounded the copper plumbing. The branch...

Wiring from my house panel to my pole barn panel [ 1 Answers ]

I am going to be wiring my pole barn up soon and just need some help on the type of wire to use. In my house I have a 200 AMP service and plan on running a 100 AMP feeder from that panel to my subpanel in the barn. (Just under 100 Feet) I am going to run a 6 gauge ground, two 4 gauge...

Main Circuit Panel to Branch Panel? [ 1 Answers ]

Hello experts, OK... My Main Load center in my home has a branch circuit connected to a 60 amp breaker. The branch feed wire is a 4awg copper wire. The branch panel is downstairs and it has a 100amp main cutoff breaker installed in it. It feeds the whole downstairs including... (1)...


View more questions Search