    Condenser Fan Motor Thermal Overload
    I know this has been asked many times, because I read through many forums when I discovered this problem this weekend. My upstairs 4-ton Lennox condenser fan motor was tripping its thermal overload after about one hour of operation. I swapped the motor, fan, and the 7.5 ufd run capacitor with the downstairs 5-ton unit (both motors are 1/3 HP 1075 RPM). The replacement also tripped its thermal overload, again after about an hour. One forum suggested that this problem could be caused by the indoor filters, dampers, and registers. Out of desparation, I changed the filter (dirty, but not that dirty), and opened the 4 registers (out of total 10) that had been closed. This seemed to fix the problem. As a final check, I measured the voltage at the contactor, and saw 247 VAC (using two different meters).

    I don't really want to go back and re-create the problem, but what was really the major contributor? BTW, the voltage is still high.
    bitters's Avatar
    bitters Posts: 348, Reputation: 12
    Full Member
     
    #2

    Jul 28, 2014, 11:35 AM
    247 Volts is OK, that's what the power is in my area. Was it cooling the house before it started tripping? I don't think the filter and registers would have any effect on the motor, at least I have never seen that happen. Maybe some one will come along and correct me. Did you see any frost on the pipes? BTW, is this a heat pump?
    Houston549's Avatar
    Houston549 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 28, 2014, 03:01 PM
    This is a 15-18 yr-old Lennox 12ACB48 plain-old A/C, with original Copeland scroll compressor. The suction line was cold and sweaty (but not frosty), prior to the trips, and the unit was cooling well. The forum that suggested the filter and registers as being a problem, may have said so in the context of freezing up the evaporator, but I didn't look at the evaporator, so I can't say if that was the case here or not.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Conderser fan motor quits on thermal overload [ 2 Answers ]

IT runs for about three or four min. and quits. The old motor would not run at all it's a new motor and capacitor. The contact voltages checked good. The only thing left is the thermister and the control board. The thermister does get pretty warm. Please help

Replacing a Rheem 5 wire condenser fan motor with an Emerson 4 wire condenser Fan [ 0 Answers ]

I have a Rheem a/c unit that the fan motor quit. I took all the information off the old motor and went to a local supply store and they cross-referenced the numbers and gave me and Emerson motor. All the specs are the same, 1/5 HP, 1075 RPM, 60 Hz, 1.3 Amp, single phase. When I got home, I took...

Trane condenser fan motor to A.O.Smith condenser fan motor [ 2 Answers ]

The Condenser fan motor I removed from a Trane unit had four wires 1 black, 1red, 1brown and . The black wire went directly to #3 on the relay, the red wire went to the capacitor with black wire from #6 on the relay the brown wire went alone to the other side of the capacitor. I purchased...

Outdoor condenser fan goes into thermal protection mode [ 3 Answers ]

My outside unit condenser fan motor would run fine, when pushed by a screwdriver, or the like, but would not start on it's own. I replaced the motor with the IDENTICAL unit, name brand and all, but the wires were different. I also replaced the capacitor. As it turns out, the capacitor they sold me...

Why does a condenser fan go off on overload [ 2 Answers ]

I put in a brand new fan motor & capaciter that matches perfectly with the one I removed But it goes off on internal overload after 5 minutes. What could be my problem!


View more questions Search