Ultra Member
|
|
Jun 22, 2014, 09:07 AM
|
|
Testing a outlet
MultiMeter AC setting. Put the red probe in the right slot and the black in the left slot. Got a reading of 1. Then put the black lead into the oval slot and got a reading
Of 1.
Do you think it's the receptacle?
|
|
 |
Printers & Electronics Expert
|
|
Jun 22, 2014, 12:29 PM
|
|
You got a reading of 1 volt? No at this point I do not believe it s the receptacle. If you CA approximate the mid point of the circuit, between the failing receptacle and the circuit breaker, test a that point and then work your next test point in either direction until you isolate the failure.
|
|
 |
Ultra Member
|
|
Jun 23, 2014, 03:36 AM
|
|
Thanks don. The outlet in the bedroom has a conduit with just two wires. The pipe just ends there. The tester on the bare wires show 1-5
Volts. All the other outlets in the house works.
|
|
 |
Printers & Electronics Expert
|
|
Jun 23, 2014, 11:34 AM
|
|
If there are only two wires to the receptacle, then that receptacle is on the end of the branch circuit. What is on the rest of the circuit?
Do you know which circuit breaker controls that circuit? If so, have you tried to reset the breaker. Sometimes a breaker will trip even though the handle will appear to be in the "On" position the breaker is off.
Try pushing the handle as far to the off position as possible and then switching it back on.
|
|
 |
Ultra Member
|
|
Jun 23, 2014, 11:45 AM
|
|
I will try resetting the breakers. The rest of the circuit is working.
|
|
 |
Ultra Member
|
|
Jun 23, 2014, 11:55 AM
|
|
Pastor, What range of voltage is the multimeter set for? Could you actually be reading between 100 and 150 volts maybe?
What happens if you plug in just a regular lamp?
|
|
 |
Ultra Member
|
|
Jun 23, 2014, 01:43 PM
|
|
Just no power at all. Tried various items electric razor lamp, meter is acv
750 -200 just on the bare wires themselves only showed 1-5 volts
|
|
 |
Uber Member
|
|
Jun 23, 2014, 02:36 PM
|
|
If it is a Harbor freight tester, the voltage switch is 0-200 and 0-750. Default is 1 volt for continuity check. No voltage to the outlet.
|
|
 |
Ultra Member
|
|
Jun 23, 2014, 03:25 PM
|
|
Attachment 46180 Yes it is a harbor freight item set on acv 750-200
|
|
 |
Uber Member
|
|
Jun 23, 2014, 05:25 PM
|
|
Look at your setting switch. It is EITHER 0-200 or 0-750.
|
|
 |
Ultra Member
|
|
Jun 24, 2014, 03:32 AM
|
|
Meter show the rest of the outlets at 226-220 volts. There is no voltage
In these two wires. I do not know why?
|
|
 |
Ultra Member
|
|
Jun 24, 2014, 03:47 AM
|
|
Put a nightlight last night in the outlet. At 2 A.M. it came on.
Now the outlet suddenly has power. Reads 120 Volts. Must be something loose
Somewhere?
|
|
 |
Uber Member
|
|
Jun 24, 2014, 10:16 AM
|
|
Pull the outlet and check the wires. If they are stabbed in the back, that is possibly the problem. Rewire using the screw terminals.
|
|
 |
Uber Member
|
|
Jun 24, 2014, 10:17 AM
|
|
 Originally Posted by pastor1189
Meter show the rest of the outlets at 226-220 volts. There is no voltage
In these two wires. I do not know why?
I hope not!! 120-126 would be logical.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Testing for amps in an outlet
[ 2 Answers ]
What setting do I use on my multimeter to test for the number of amps available in an outlet. For example, I want to see if a kitchen plug is split with 15 amps up and 15 amps down.
Thanks,
Erik
Outlet testing as open ground
[ 2 Answers ]
History:
Bought the house a few month ago, there was a TWO prong outlet over the mantle that I want to plug my TV into but it didn't work. I didn't put a tester on it until after I tried replaced it but I used a working lamp and it didn't work.
Now:
I bought a surge supression outlet ($20 a...
Testing outlet amperage with multimeter
[ 2 Answers ]
Can you test the actual amperage of a 120v home outlet with a multimeter?
When I plug in an appliance over 10amps in the 15amp outlet, the GFI kicks off. I want to test the outlet to see exactly how many amps are available. Thanks
Testing 220v outlet
[ 3 Answers ]
Hello!
I have a 4 wire outlet in the garage which is used for a generator. Wire colors are Black, Red, White, and a Copper wire wrapped in paper. All the wiring is contained in a metal conduit.
I just purchased a heater for the garage and it had a 3 wire plug. I disconnected the conduit,...
Testing an electrical outlet
[ 13 Answers ]
When testing an electrical outlet with a circuit tester and all three lights come on, what does that mean and how do correct it?
Thanks,
Mike
View more questions