    Hot Bare Wire
    Trying to install security lights and found a 3-wire in the attic. The bare wire and the white wire complete a circuit. What can I do?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    May 5, 2014, 07:06 PM
    It is possible the white wire is hot if it is part of a switch loop. Where does it connect? Where does it come from? What is the other wire-you mentioned 3.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    May 5, 2014, 07:54 PM
    What is the third wire?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    May 6, 2014, 06:47 AM
    Just exactly how do the white wire and the bare wire complete the circuit? "Bare" is the
    Equipment grounding conductor and is NOT part of the circuit.

    A normal circuit is made up of a hot conductor (usually black) and a Neutral conductor (usually white)

    The bare conductor keeps all of the metal in the circuit at the same potential level so you do not get a shock if you touch the metal. It also functions to clear a fault or short circuit.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #5

    May 6, 2014, 06:55 AM
    Quote Originally Posted by donf View Post
    Just exactly how do the white wire and the bare wire complete the circuit? "Bare" is the
    Equipment grounding conductor and is NOT part of the circuit.

    A normal circuit is made up of a hot conductor (usually black) and a Neutral conductor (usually white)

    The bare conductor keeps all of the metal in the circuit at the same potential level so you do not get a shock if you touch the metal. It also functions to clear a fault or short circuit.
    If the white wire was hot from a switch loop, the ground would complete the circuit and measure 120 on a VOM if white and ground connected.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    May 6, 2014, 07:40 AM
    Agreed, but the OP did not provide a full description of the wiring. If the supply is going directly to the switch, then a 120 v between the supply's neutral and the bare EGC would indicate a serious problem.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hampton bay ceiling fan wire diagram no bare wire [ 1 Answers ]

Putting up a ceiling fan, unsure what to do with the green. I live in an older home and there is no bare wire at the box.

Why does my 8 3 wire with ground have a bare coper wire [ 7 Answers ]

I am installing a range with 8/3 with a ground it has a red-black for hot white for nutral, green for equipment ground bar and a bare copper wire ground. The receptical has red/black/green/white but no place for the bare wire to hook to. Should I cut this off or hook it to the green

Bare copper wire; [ 3 Answers ]

Bare copper wire; Why do we use bare copper wire for grounding, why not all insulated?

Using the ground or (bare) wire for the neutral wire [ 2 Answers ]

I have a problem with some wiring that I ran for an outside motion light. Although the hot leg and ground wires are fine, the neutral wire is defective ( it may have gotten knicked or something). Of course, now the wiring is covered up behind a wall that I do not want to tear into if it can be...


View more questions Search