Junior Member
|
|
Apr 10, 2007, 04:20 AM
|
|
Wiring for a ductless unit
I have a 15KBTU mini split unit and the data calls out for 14/3 wire to run 220V, 15 Amps to the condenser. This seems kind of light to me but this is what is called for. My run is going to be around 90'-100', should I use heavier wire, say 12/3?
Thanks.
|
|
 |
Home Repair & Remodeling Expert
|
|
Apr 10, 2007, 07:27 AM
|
|
It won't hurt to move up to 12/3 or even 10/3 for future equipment. They don't normally expect a 100 ft run, too much line drop.
|
|
 |
Full Member
|
|
Apr 10, 2007, 12:01 PM
|
|
Most 15,000 btu/hr, 230 volt mini split condensing units only use about 8 amps. 14/3 is normally rated at 15 amps so 14/3 should work fine but it never hurts to go bigger.
|
|
 |
Junior Member
|
|
Apr 11, 2007, 10:09 AM
|
|
I'm going to go with 12/3 and a 20 amp breaker. Do I need to put a disconnect switch next to the outdoor unit or am I okay with just the breaker inside the house?
Thanks.
|
|
 |
Home Repair & Remodeling Expert
|
|
Apr 11, 2007, 10:13 AM
|
|
That would be the safe way to do the installation. You could just install a sub panel. Is this a garage, barn, work area being connected to a home?
|
|
 |
Full Member
|
|
Apr 11, 2007, 12:53 PM
|
|
Electrical code requires a disconnect means within sight and readily accessible. NFPA 440-14
|
|
 |
Junior Member
|
|
Apr 11, 2007, 02:16 PM
|
|
This is for a bonus room in my attic. I installed a sub panel in the room and I'm going to wire the mini-split off it. I think I'd just go with a disconnect switch/box and nothing more than that. I don't think I need another breaker or anything like that within sight and readily accessible.
Thanks.
|
|
 |
Full Member
|
|
Apr 11, 2007, 03:27 PM
|
|
That's your option but, if you ever decide to sell your home and need a electrical inspection done, it will be a electrical code violation. It also helps the service technician when servicing the unit and provides a way to shut the unit off in case of an emergency if no one is at home.
|
|
 |
Uber Member
|
|
Apr 12, 2007, 02:46 AM
|
|
A circuit breaker in the panel is required, and a switch at the outdoor unit will suffice.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Outside unit doesn't come on when thermostat turns inside unit on so no heat?
[ 1 Answers ]
My thermostat will trip my heater to turn on. The inside blower turns on but the outside unit doesn't turn on. I can get it to go by turnign off the unit at the thermostat and waiting a minute. I turn it on and off until I hear the outside unit turn on. The problem is when the Thermostat turns if...
Heating unit
[ 1 Answers ]
How do you get the squirrel cage from the air duct blower motor
Old window unit
[ 1 Answers ]
We have a Friedrich window unit. It has a 3 prong plug and we have it in a 20 amp socket. The breaker is a 60 amp and the wiring is 220 12/3. We aren't getting power to the unit. What are we doing wrong here?? :eek:
View more questions
Search
|