    Service entrance cable.
    What is the proper size SER cable to run from the meter panel (with 200 amp breaker disconnect) to the inside breaker panel (150 amp). Is it 4/0 4/0 2/0 (three conductor) or is it 4/0 4/0 4/0 2/0 (four conductor)? I'll have the whole installation inspected by a licensed electrician before calling the city but wanted to make sure this meets new code before going forward.

    Thanks
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Mar 8, 2014, 06:07 AM
    I don't understand your question. Is your service going to be 200 Amp or 150 Amp?

    Personally, if you are going to have POCO bring 200 amp to you, why would you step down to 150, use the 200 Amp.

    As to the cables. PCOC will use a 4/0 three wire cable to bring the service to your meter. Now, If the meter is going to serve as a "Main Disconnect" switch, then you must use a four wire cable from the disconnect switch to the distribution panelboard.

    Now the cable from the disconnect switch is determined from NEC (2011) Table 310.15(B)(16). You need to know the temperature of the connections of both the disconnect switch and the distribution panelboard. If either device is rated at 60(C), then column #1 (Aluminum) must be used. Which results in a 4/0 AWG cable size for 150 Amps. If you use 200 Amp, then you need a 350 kcmil cable. Again, you would be smarter to wire for the 200 Amp service even though you are only getting 150 Amp. This will allow you to use the same cable if you should decide to go to 200 amp at a future time.

    However, if both the disconnect switch and the distribution panelboard are listed for 75(C) then the conductor size is determined from column #2 (center) Aluminum column. For 150 Amp, use a #3/0 AWG cable. For 200 Amp use a 250 kcmil cable.

    Be careful here. Because you are using a "Main Disconnect" switch, Neutral and Ground must be bonded together at the disconnect switch. At the distribution panelboard, Neutral and Ground cannot be bonded. Neutral must be isolated from Ground.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Mar 8, 2014, 06:27 AM
    Don, Don, Don. You are way over thinking this.

    He is asking about SER. This is the proper cable from an outside disconnect to an inside panel.
    Since we can assume this is for a residential application, and we can also assume this is for the main panel <"from the meter panel (with 200 amp breaker disconnect) to the inside breaker panel">, we would use the table for sizing residential service entrance.
    This would be 4/0AL or 2/0CU for a 200A service, which this is. Worrying about the temperature of the terminations is not even worth the effort.

    cmkruse, I'll also ask, why a 150A panel off a 200A disconnect?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Mar 8, 2014, 07:02 AM
    Stan,

    Good morning. My over thinking was caused by the "Breaker at the meter".. I took that to be a "Main Disconnect" are you saying that that would not be true?

    If there is a main disconnect switch, don't we have to use a 4 wire feed from the switch to the panel?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Mar 8, 2014, 07:20 AM
    Yes, that's how I took it too. That there is a main breaker/disconnect at the meter. This is why he is asking about SER cable. SER has two (sometimes 3) hots, a neutral and a ground.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable [ 23 Answers ]

I am re-wiring an old house. It is a small 2 bedroom, 1 bath house. We put in a 200 amp service and need to run a service entrance cable about 20 -25 ft to the inside breaker panel. My question is how big of a gauge wire should we run for the service entance cable. #? 3 conductor with ground in...

Service entrance cable [ 2 Answers ]

Having new 100amp meter installed professionally,but I am burying wire to the building which is 125' from where meter is mounted. Will I have to upsize the size of wire because of the distance? I also intend to enclose in conduit, so I'm not worried about using "U" coded wire

Service entrance cable (alum) size for a 100 amp service at 186 feet for a garage [ 1 Answers ]

The garage is 186' from the service at the house. I wanted to make sure the voltage drop would not cause a problem.

Cable TV and Telephone New Service Entrance [ 7 Answers ]

I'm in the process of changing the location where the telephone and cable service come into my house to a new location. I was wondering if there is a proper way to correctly attach the two lines (one coax for cable and one multi conductor for telephone) coming from the overhead pole in my back...

Service entrance cable [ 1 Answers ]

Is there a code restriction on the footage of service entrance cable from the triplex to the meter socket ?