    Furnace problems
    I have a Bryant plus 90i furnace that stopped working. Upon inspection, the flashing lights showed a 42 which states that the inducer outside valid speed range. I replaced the inducer motor, main control board and the 2 stage pressure switches. I also pulled a rag through the exhaust PVC line to make sure it was not plugged. Reset control board as instructed by manufacture and lights still blink 42. I then took apart all the drain hoses and made sure they were not plugged. Still the same code, 42. Since all of the major parts were replaced with new ones, I am at a loss as to what to check next.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Dec 21, 2013, 12:49 PM
    I too am at a loss other than to suggest you check incoming voltage. It should be +/- 120 volts AC. If it is over 130 or less than 110, call an electrician.

    Last second thoughts:
    I wonder if the heat exchanger is plugged. If it is, it would cause an air restriction & could throw the inducer speed off.
    If you have an air intake pipe, check it for blockage as well.
    Make sure no hoses are cracked.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Thermostat problems or furnace problems [ 22 Answers ]

Is it possible that a thermostat operates correct all the time except when it reaches the temperature that is set doesn't maintain that temperature?:D I noticed that actually that thermostat gives a signal to the furnace but furnace doesn't turn on but that happens only when thermostat needs to...

Thermostat problems or furnace problems [ 0 Answers ]

I own a rite temp pure comfort heater 33,000 BTU for the basement. Model rtn300tq. It lights up but quits before it gets to the correct temp. What should I replace don't have sufficient funds for commercial repair. What termostat number and thermocouple are used on this model pete 586 755 5453

Furnace Problems [ 21 Answers ]

My furnace stopped coming on when it was supposed to. I have replaced the ignitor and the thermostat. It comes on blowing hot air and the house gets warm then it won't come on for almost another hour when the house is freezing by then. If it is sixty in the house it should come on when I set it to...


View more questions Search