    6-2 w ground
    I need a 220 volt sub panel about 80 amps.. it says for the common to be shielded like the 2 hot wires... the 6-2 is 6 gage but the ground is about a 8 gage.. is it OK to cover the 8 gage wire a few layers of tape to shield it ? Will the 8 gage be OK as a common with the 2 how wires being #6 ?
    Yes I will have a separated ground going to a ground rod... thank you
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Nov 25, 2013, 05:08 AM
    Wow, wow, wow. A lot wrong here. Please do not do anything until you get this sorted out.

    6/2 is not good for a sub-panel. The bare wire is a ground, not a neutral, and can never be used as a neutral.
    You must used 6/3 with an insulated white neutral, and the neutral and grounds must remain on separate bars in the panel with the bond screw not installed.
    The ground rod is not what gives you your equipment ground.

    Also... #6 is not enough for 80A. You need #4cu wire, or 4/3nm cable.
    And you still need a ground rod.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Nov 25, 2013, 09:50 AM
    If you are setting this panel in a separate building, you will not be allowed to use type NM cable.

    You will have to use a cable type that is listed for the environment that the cable will be installed in.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Can I splice tap a new ground bus bar to an existing ground wire? [ 3 Answers ]

I am installing a new ground bus bar for telecom equipment grounding in an existing building. There is an existing ground cable coming from and existing transformer and down into the slab. The grounding point is nowhere to be found. Hence, the question whether it is acceptable to splice tap the...

Can I ground my generator to a copper rod driven into the ground with coax cable? [ 2 Answers ]

I am going to test my 6000 watt generator. It is recommended that I ground it to a copper rod driven into the ground. I alread have a copper rod that is used to ground my telephone and cable lines. Can I use a length of coax cable to run from my generator ground to the copper rod?

What size ground wire do I need for a 10 mega-Hertz ground 400 feet long? [ 1 Answers ]

We are adding a new ground that is 400 feet away, and we need to size it for 10 mega-Hertz. Can you please tell me the size cable that we need to install?

Can a receptacle ground be attached to white nuetral terminal for ground? [ 1 Answers ]

I have older house. The receptacle showed "open ground." I connected a wire from the green ground terminal to the nuetral terminal, and the meter read "correct." I left it that way because everything worked. Is it safe?

Nec-covering of ground wire from the ground rod to the water pipecables [ 1 Answers ]

I installed a new service meter panel and ground rod. The ground rod is connected to the meter panel via a #4 copper wire to a water pipe located 10 feet away. Is is allowable to bury the #4 wire between the ground rod and water pipe to keep it from being a trip hazard and protect the wire? ...


View more questions Search