    100 amp panel and wire
    royterk - is asking - I have reviewed several similar questions, however I am still a little confused. So, I will be running wire from my 200amp house panel to my new garage. This will be either direct burial or run in a 11/2" PVC schedule 40 conduit. I was told by an electrician whom I respect that I should put a 100amp panel in the garage. The anticipated use of electricity will be for lighting, garage door openers (2) and general plug in equipment (nothing to elaborate. What kind and size wire should I use from house panel to garage panel? Aluminum or copper? Keep in mind that future use may need more power than I intend to use right now.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Nov 5, 2013, 11:46 AM
    The first question to ask is whether your panelboard will accept a 100 amp breaker. You should have that information in the documentation that came from the panelboard's manufacturer.

    The next question is what are the listed temperatures of the main service panelboard and secondary panelboard.

    If both are listed for 75 (C) then either #3 AWG Copper or #1 AWG Aluminum may be used, However, if either or both are listed for 60 (C) then #1 AWG Copper or #1/0 AWG Aluminum are your choices.

    Next, how far from the panelboard is the garage and is the garage attached to the home? If the distance is greater than 100 ft. you would be wise to check for voltage drop issues.
    royterk's Avatar
    royterk Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 5, 2013, 12:53 PM
    The house panel will handle a 100amp breaker. The distance from the house panel to the garage panel is approximately 30 feet and is detached. The wire needs to be underground. I am not sure what AWG means. Is it okay for direct burial? Someone suggested UF #2 copper wire. Is that acceptable. Panels are listed for 75 (C).
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Nov 5, 2013, 01:02 PM
    "AWG" American Wire Gauge - the size of the cable.

    "UF" is a type of insulation that is listed for use in the 60 (C) temperature only. #2 AWG is listed for 95 amps, not 100 amps, so the answer is no.#1 UF would work.

    Personally I'd use USE cable as that is listed for 75 (C).
    royterk's Avatar
    royterk Posts: 3, Reputation: 1
    New Member
     
    #5

    Nov 5, 2013, 02:37 PM
    My final shot at this is as follows. After seeing all the information on the web I have concluded that all I need is a 60am panel in the garage. That said, I need to know which wire I should use (size and designation) for direct burial. Don - thank you for your help.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Nov 5, 2013, 03:36 PM
    It's not that simple.

    60 amp will require a 4 wire cable. If you are using copper, then a # 6 conductor listed for wet conditions. If you use UF, then you must use a # 4 UF cable will be needed.

    Because the garage is separate, you must have a grounding system setup at the garage.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size required from 200 amp main to 100 amp sub panel [ 1 Answers ]

The sub panel is located @75 feet from main panel.

Wire size for feeder for 100 amp sub panel 100 ft from main. [ 0 Answers ]

I majored in sociology, so please bear with me... I am building a 400 sq ft out building with 2 1500 watt heaters, a small kitchen including a small range, small dishwasher and fan hood. There will also be a 30 gal hot water tank, and a .1/2 hp sewage ejection pump. My calculations so far...

4 wire 100 amp panel [ 6 Answers ]

My 100 amp panel has a 4 wire feed. 2 hot wires to the 100 amp breaker and the netural and ground wire go to the same ground bar which is grounded to the panel. I this correct or should there be a separate ground and a separate netural bar? The panel is original to the house built in 1987. The 100...

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...

Wire UF wire to run to new 100 amp service panel? [ 10 Answers ]

My house has a 200 amp service. I have a new 30x40 building in back. I have a 100amp Square D load center for the building. I want to run a line from the house to power the building. Big items include, air comp 30 amps, welder 50 amps, other raidial arm saw, ban saw pipe saw 15-20 amps? It is...


View more questions Search