Oct 2, 2013, 05:36 PM
|
|
Main burners
I have an intercity gas forced air furnace. IT has a Honeywell spark ignition control module. The pilot light lites, but the main burners will not come on. The flame sensing rod is clean and appears to be in the flame. I am getting 24 volts to the gas valve. I suspect the gas valve or could it be in the module? I figure that if I am getting spark and pilot light and 24 volts at the gas valve, then it is the valve? What do you think?
|
|
 |
Ultra Member
|
|
Oct 3, 2013, 07:19 PM
|
|
If you are getting 24v to the gas valve & no main burner, most likely the gas valve is at fault. Silly question I know but I have to ask: Is the switch on the valve turned on?
|
|
 |
New Member
|
|
Oct 4, 2013, 04:41 PM
|
|
 Originally Posted by Grady White
If you are getting 24v to the gas valve & no main burner, most likely the gas valve is at fault. Silly question I know but I have to ask: Is the switch on the valve turned on?
Thanks for the input. Yes, the switch on the gas valve is in the on position(one of the first things I checked) but thanks for asking. Not a silly question. I did furnace work for 6 years, but has been 5 since I have done any and am helping a friend. He had someone come look at his furnace and they are trying to rip him off by charging an outrageous amount. Thanks
|
|
 |
Ultra Member
|
|
Oct 4, 2013, 05:54 PM
|
|
Since that furnace is a spark to pilot ignition system, the gas valve should have 3 terminals. They would likely be marked MV (main valve), PV (pilot valve) & MV/PV (common).
Are you getting 24v between MV & MV/PV? If you are not & the spark does not stop, the system is not sensing the pilot flame.
|
|
 |
New Member
|
|
Oct 7, 2013, 06:09 PM
|
|
 Originally Posted by Grady White
Since that furnace is a spark to pilot ignition system, the gas valve should have 3 terminals. They would likely be marked MV (main valve), PV (pilot valve) & MV/PV (common).
Are you getting 24v between MV & MV/PV? If you are not & the spark does not stop, the system is not sensing the pilot flame.
I am sure that I was getting 24v between MV & MV/PV but will double check to make sure. The pilot did light( there was flame) however the spark did not stop. I'll check the sensing rod to make sure it is the flame where it needs to be. Thanks.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Main burners on furnace do no ignite
[ 8 Answers ]
I have a bryant furnace, model 398. The main burners do not light after the pilot light ignites. I have cleaned the blower motor and everything else I can. Everything looks and sounds good, but the main burners are not getting any gas to them and lighting. Its getting cold in here and need some...
Main Burners
[ 0 Answers ]
How do you check and clean the main buners on a 58sta135-16
Armstrong SX 80 Furnace will not light at main burners
[ 3 Answers ]
This will be our second fall/winter in this house and our Armstrong SX 80 furnace with a Honeywell smartvalve ignition system will not light. The ignition switch will come on, but no gas is being emitted so the main burners will not light. I have seen this before where the sensor is bad after the...
Main burners never ignite
[ 1 Answers ]
Lennox G20 Series gas furnace - Igniter works, ignition flame is starts, but the main burners never ignite. Blower fan starts after appropriate period. What is wrong?
Main burners on my carrier furnace not lighting
[ 1 Answers ]
I have a carrier natural gas furnace, model no. 58es080-30. The pilot light ignites, then you can hear a clicking noise, after about 15-20 seconds the blower fan starts up but the main burners are not lit. The furnace has acted like it's been having trouble igniting in the past few weeks, seems...