    Elkhunter's Avatar
    Elkhunter Posts: 3, Reputation: 1
    New Member
     
    #1

    Sep 17, 2013, 02:26 AM
    230 volts compressor
    I just got for my walk In cooler an conpressor with condensing unit. The conpressor tag says 230 volts 60 hz 1hp single phase motor with max fuse 15 amp. I was figuring of running about maybe 20 ft of 12-3g from a double pole 15 amp breaker In the panel to hardwire to the compressor and condensing units wiring box. It's a older machine and I just wanted to make sure this was correct way to hardwire it in. Any suggestions? Thanks for your time
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Sep 17, 2013, 04:18 AM
    Unless you are less than 50 feet and within sight of the panel, you should install a disconnect at the equipment. What type of wiring are you using? Just a guess, but it sounds like MC cable or conduit would be appropriate. (If this is a business avoid using romex)
    Otherwise, it sounds like you're OK...
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Sep 17, 2013, 04:55 AM
    This is a walk-in? I assume it's a commercial setting?

    Your best, and probably only, bet is to hire an electrician to do this. You should not be doing electrical work on a commercial place. Your own home is one thing if you don't really know what you are doing, but a commercial place where there will most likely be many people on site is not acceptable.
    Elkhunter's Avatar
    Elkhunter Posts: 3, Reputation: 1
    New Member
     
    #4

    Sep 17, 2013, 07:33 AM
    Thanks for responses. This is not a commercial walk I'n cooler I'm a big time hunter I process my own meat. This is for personal use. What would be a adequate service disconnect. I have 12-3 romex and 12-3 wire for"wet" locations to be run I'n conduit. Thanks again
    Elkhunter's Avatar
    Elkhunter Posts: 3, Reputation: 1
    New Member
     
    #5

    Sep 17, 2013, 07:46 AM
    Quote Originally Posted by Elkhunter View Post
    Thanks for responses. This is not a commercial walk I'n cooler I'm a big time hunter i process my own meat. This is for personal use. What would be a adequate service disconnect. I have 12-3 romex and 12-3 wire for"wet" locations to be run I'n conduit. Thanks again
    I am less then 50 feet max is 20 feet and the electrical panel is outside the cooler door like 8 feet. Cooler is 8 by 10 by 8 ft tall with a 5th by 8ft room with the electrical panel. This pretty much matched the existing length of shed and a place to hang gambels and scales and other things. The compressor and condensing unit is outside of the cooler itself I'n a little 4 ft by 4 ft room on back of cooler. A copper tube runs from the unit to a cooling fan inside the cooler. Thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

On 208/230 3phase is it OK to have 70 volts to ground on L1 on L2 130 on L3 129 [ 3 Answers ]

On 3 phase 208/230 power is it OK to have 70 volts to ground on L1,on L2 130 and on L3 129

Can I run a 208-230 volts 1/3hp 60hz, model no ka55hfxcl-240 nfg k91c on a 110 or [ 3 Answers ]

I have a mobel home furnace blower motor that is a 208-230 volts I want the motor to run on a 120 if I can , it has four wires red,black orange and brown thank you

Wiring 230 volt air compressor [ 1 Answers ]

I am wiring a 230 volt air compressor 3.5 hp to my shop.The delima is my shop is 300 feet from my house breaker box. Is it possible to pull enough power that far to run the compressor safely? Maybe I should just get 300 feet of air hose. LOL

Bose wave radio connected to 230 volts [ 1 Answers ]

Bose wave radio brought from US, which works on 120 Volts AC was connected directly to 230 Volts AC in India. The radio does not turn on now. Any suggestions for next action?


View more questions Search