I have a new mobile home 200amp service and I have built a pedestal and am installing both a meter box and a service disconnect which is about 42" from the trailer. Every website I have found recommends 2/0THHN copperwire for the two hot leads and 1/0 copper wire for the neutral. Is this correct or do I need different sized wire?
|
|
 |
Uber Member
|
|
Aug 9, 2013, 08:03 AM
|
|
That's fine for 200 Amps.
|
|
 |
Printers & Electronics Expert
|
|
Aug 10, 2013, 07:13 AM
|
|
Since the service point will outside of the trailer, you cannot use THHN type conductors.
THHN is listed for use in "Dry" locations only.
THHW is listed for Wet areas, also THWN-2, XHHW and XHHW-2. All of these would have to be in conduit.
Using a multi conductor cable listed for direct burial (Type USE) is also a better choice.
|
|
 |
Printers & Electronics Expert
|
|
Aug 10, 2013, 09:05 AM
|
|
One more thought, because you are putting in a main disconnect switch at the meter, you cannot use Table 310.15(B)(7) to select your service entrance conductors 200 amp - 2/0 cable.
You must use a 4 wire connection from the disconnect switch to your service panelboard. Which means that you need to use Table 310.15(B)(16). A 200 Amp feed requires a 3/0 cable if both the switch and the panelboard are listed for 75 (C) {167(F)}. If they are not listed for that temp, then you have to use the 60 (C) column which means that you would need a 250 kcmil cable.
|
|
 |
Uber Member
|
|
Aug 11, 2013, 03:25 PM
|
|
I am guessing/assuming the wire was THHN/THWN, as that is what most Electrical Supply House carry.
Insulation is Important.
|
|
 |
Electrical & Lighting Expert
|
|
Aug 11, 2013, 03:39 PM
|
|
Since the service point will outside of the trailer, you cannot use THHN type conductors.
THHN is listed for use in "Dry" locations only.
THHW is listed for Wet areas, also THWN-2, XHHW and XHHW-2. All of these would have to be in conduit.
I realize this is a very popular thing to correct on message boards, but these days it is a non-issue. Most people just say THHN as a matter of habit, and pretty much all THHN is also dual rated THWN these days.
|
|
 |
Electrical & Lighting Expert
|
|
Aug 11, 2013, 03:41 PM
|
|
One more thought, because you are putting in a main disconnect switch at the meter, you cannot use Table 310.15(B)(7) to select your service entrance conductors 200 amp - 2/0 cable.
You must use a 4 wire connection from the disconnect switch to your service panelboard. Which means that you need to use Table 310.15(B)(16). A 200 Amp feed requires a 3/0 cable if both the switch and the panelboard are listed for 75 (C) {167(F)}. If they are not listed for that temp, then you have to use the 60 (C) column which means that you would need a 250 kcmil cable.
Don, just because there is a switch outside does not mean these are not still the main power feeder conductors. NEC 2011 Table 310.15(B)(7) still applies.
Remember, this table is for "Single-Phase Dwelling Services and Feeders"
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Mobile home wiring
[ 2 Answers ]
I own a palm harbor 4 bedroom double wide. The front bedroom and the living room outside wall are without power. There is power coming out of the breaker box but stops before reaching there. Someone told me it is in the crossover. What do I look for to fix this problem?
External Mobile Home wiring
[ 2 Answers ]
I have 200 amp service poll with a 200 amp breaker box mounted on the poll, there are 3 wires from the meter to the box. One ground and 2 120 amp. No neutral wire. The poll has a ground wire in the ground beside it that the ground wire in the box is connect4ed to. I want run a line from bottom of...
Wiring a mobile home
[ 4 Answers ]
I'm running the service for my trailer and I need some help with it. I have a 200 amp panel in the home and a 200 amp panel on the pole. But the panel on the pole only has one set of lugs on the top of the main breaker. Do I need lugs on the bottom of the panel to put the wire in from the trailer...
View more questions
Search
|